Pump it up!
We bought a field that is rather wet, and close to the level of the river. We want to transform it into an orchard. So after some searches and discussions, I installed an off-grid solution to “pump it up”!
2 solar panels, giving me 750Wc
MPPT 100/20 48V
SmartShunt
GlobalLink 520
Inverter 24V 500VA 230V
Battery Load Balancer
4 x 50Ah Redodo batteries
The pump takes about 200W, so I have roughtly 8h of reserve
And I added a relay for future extension for a watering pump for summer.
A LOT of fun, and it works flawlessly for 3 months now!
The hut in the forest … ;
In this humid environment, an earth electrode and a residual current circuit breaker should also be used.
Actually, it is on the south edge of a forest, so there are around 6 hours of full sun. The picture is very partial :slight_smile:
Thank you for the tip of the earth electrode and residual current CB, I will investigate that idea!
Absolutely necessary for the function !!!
3.5 Connecting the inverter neutral output to the chassis/ground
The AC output is isolated from the DC input and the chassis. Local regulations may require a true neutral. In this case one of the AC output wires must be connected to the chassis, and the chassis
must be connected to a reliable ground: see appendix A
The chassis is in wood, would it work?
Just kidding…
I’ll add a ground bar and line this week-end
Then they have to change the instructions also for wooden huts … in the forrest
The AC supply from the inverter has no reference to earth, it’s an isolating transformer. Linking neutral and earth can make the system less safe as you then require an RCD to detect live to earth faults.
Are you using any tank sensor connected to the Cerbo? Which one?
Thanks
Hi Josep, I am using a GlobalLink, no Cerbo. I was thinking about installing a tank sensor to check the level of the pond, but realized it has little benefit: if the water is high and the battery are loaded, then the pump kicks in. If the water is low OR the batteries are low… it does not. I was more thinking about a remote, 4G, camera, to check the pond, the sheep and check if nobody was trespassing in my property…