I had a conversation with Grok feeding the information provided by you to help me come up with a plan. Sorry for the long post but this is Grok’s suggestion.
Set-and-Forget Mode: Solar/Battery Priority with Automatic Grid Fallback
Objective: Configure a Victron system for a Jayco Pinnacle 32RLTS RV to prioritize solar/battery for all AC loads (860W average, including RV’s AC-to-DC converter for 12V loads) in grid-connected, boondocking, and winter storage scenarios, with automatic grid fallback for low SoC/high load and manual override for 100% charging (e.g., storm prep). No mode changes needed across use cases.
System Details:
• Inverters: 2x MultiPlus-II 48/3000/35 (paralleled, 6,000W AC output, 70A charging).
• Solar: 2x SmartSolar MPPT 150/100, 2,000W array (~8,000Wh/day summer, ~4,053Wh/day winter in RV storage lot).
• Batteries: 4x EG4 48V 100Ah LiFePO4 (19.2kWh usable, CAN-bus BMS to Cerbo GX).
• Monitoring: Cerbo GX with GX Touch, DVCC enabled, VRM portal.
• Other: Orion DC-DC (48V-to-12V trickle for 12V house battery), Maxpeedingrods XP4000i generator (~3,360W on propane).
• Loads: 85W constant in storage (~2,040Wh/day), 860W average camping (260W baseline + 600W A/C, ~20,640Wh/day).
Mode Description:
• Uses Virtual Switch (VS) with Generator Assistant (repurposed for shore power) to ignore 50A grid input when solar/battery are sufficient, forcing inverters to “push” AC from battery/solar to all loads (RV’s AC-to-DC converter for 12V, A/C, etc.).
• Grid-Connected: Ignores grid if SoC >50%, solar >500W, load <4,000W. Reconnects for charging if SoC <40%, load >4,000W, or voltage <52.0V. Solar charges to 100% SoC when able; grid avoids 100% unless manually overridden or 7-day timer triggers (for EG4 balancing).
• Boondocking/Storage: Inverters power all loads from solar/battery; solar charges to 100% when possible. Shutdown at ~48V (~10-20% SoC) protects batteries.
• Override: Manual grid charge to 100% via Cerbo GX for storm prep (e.g., grid outage risk).
• Benefits: Seamless across scenarios, maximizes solar (~8,000Wh/day offsets most loads), minimizes grid, protects battery health via BMS/DVCC.
Operational Behavior:
• Solar Charging: MPPTs prioritize loads and charge to 100% SoC (56.8-57.6V absorption, 54.4V float) if excess power (e.g., >860W camping, >85W storage). DVCC ensures EG4 BMS safety.
• Grid Charging: Only when SoC <40% or other triggers; stops at ~50% SoC unless overridden or 7-day absorption timer (configurable to 10-14 days).
• Storage (Winter): Handles 85W draw (~2,040Wh/day) with ~4,053Wh/day winter solar average, charging to 100% on sunny days. Shutdown at 48V for extended clouds.
• Storm Prep: Force grid charge to 100% via Cerbo GX (~3.8 hours from 50% SoC at 70A).
References:
• Victron Solar & Wind Priority manual
• Victron Community discussions on Ignore AC/Assistants: [20] [30]
Implementation Steps
Time: 30-60 minutes (one-time).
Tools: Laptop with VEConfigure (free), MK3-USB interface ($70), Cerbo GX internet for VRM.
Prerequisites: Firmware updated (Venus OS v3.10+, MultiPlus-II v506+). Backup settings in VEConfigure. EG4 BMS connected via CAN-bus (Type A cable, Pylontech protocol).
1. Verify Firmware:
• Cerbo GX: Settings > Firmware > Check Venus OS v3.10+.
• MultiPlus-II: VictronConnect (MK3-USB) or VRM > VE.Bus > Firmware > v506+ (both inverters).
• Update via VRM (internet) or VictronConnect (MK3-USB, not iOS). \~10-15 minutes.
2. Confirm EG4 BMS Integration:
• Verify CAN-bus connection (EG4 master to Cerbo BMS-CAN, Type A cable).
• EG4 set to Pylontech protocol (LCD/DIP switches).
• Cerbo GX: Settings > DVCC > Enable, BMS Control On. Confirm battery in Device List.
3. Configure Virtual Switch and Assistants (VEConfigure):
• Connect MK3-USB to one MultiPlus-II (VE.Bus port, syncs both).
• Open VEConfigure, detect system.
• **General Tab**:
• Enable Virtual Switch (VS).
• AC Input Current Limit: 50A (RV shore plug).
• Optional: Uncheck “Switched as Group” for split-phase flexibility (test stability).
• **Charger Tab**:
• Absorption: 56.8V, Float: 54.4V (EG4 specs).
• Charge Current: 70A (35A per inverter).
• Repeated Absorption Interval: 10-14 days (extend from 7 for longer sustain).
• **Inverter Tab**:
• Low Voltage Shutdown: 48V (\~10-20% SoC).
• Restart: 52V.
• Enable PowerAssist (boosts grid for surges, e.g., A/C start).
• **Assistants Tab**:
• Add **Virtual Switch**: Enable as primary control.
• Add **Generator Assistant** (for shore power):
• Set as “Dedicated Ignore AC Input.”
• **Ignore AC**:
• Battery SoC >50% (BMS via DVCC).
• OR Solar power >500W (MPPTs).
• AND Load <4,000W (avoid overload).
• **Reconnect AC**:
• SoC <40%.
• OR Load >4,000W for >30 seconds.
• OR Voltage <52.0V for >1 minute.
• Save/upload to both inverters.
4. Cerbo GX Settings:
• Settings > VE.Bus > Confirm VS enabled.
• Add VRM widgets for Ignore AC status, SoC, solar output.
• Set VRM alerts: SoC <40%, grid failure.
• Optional: Relay for generator auto-start (SoC <20%, requires wiring).
5. Test and Monitor:
• **Boondocking/Storage**: Unplug grid—verify inverters power 860W (or 85W storage) from solar/battery, MPPTs charge to 100% if able (e.g., \~8,000Wh/day summer, \~4,053Wh winter).
• **Grid-Connected**: Plug into 50A—confirm Ignore AC (solar/battery powers loads, \~0W grid draw if SoC >50%). Test high load (>4,000W) or low SoC (<40%) to verify reconnect.
• **Storm Override**: Cerbo GX > VE.Bus > Charger > “Force to Absorption” (\~3.8 hours to 100% from 50% SoC). Verify 100% SoC on VRM/GX Touch.
• Monitor VRM for 1-2 days: Expect \~8,000Wh solar offsetting most daytime loads, grid \~0-5,000Wh/day.
Questions for Victron Community
• Is the Generator Assistant with Ignore AC the best approach for a mobile RV setup to prioritize solar/battery across grid/boondocking/storage, or is there a simpler method (e.g., modified Solar & Wind Priority)?
• Any risks with unchecking “Switched as Group” for 50A RV split-phase? Stability concerns with paralleled MultiPlus-II?
• Experiences with EG4 BMS integration via DVCC—any pitfalls to watch for?