Power Assist Mode Current limit

Hi All,

i am testing a 3x15kVA Quattros (3-phase system) with a 60kVA genset. I have noticed that the input current limit only applies or functions with a purely resistive load in power assist mode. Once we added inductive load to bring the power factor to 0.8, it no longer limits the current.

In assist mode I had the limit set to 67A which is the max of the generator based on kW rating, but when testing at around 60kVA, 48kW/36kVAR, the current just stayed at the generator’s max of 82A per phase

Does anyone have an idea of this?