Has anyone experienced a problem where parallel units within an ESS system sporadically become “unbalanced”?
The system can run for about a month at a time in a very stable manner, but about once per month, we notice the system fails to achieve the ESS grid setpoint.
Upon further investigation, it always comes down a very strange issue where much more power is flowing through one unit within a parallel set. This seems to throw off the ESS control loop.
Here’s a screenshot from the last episode of this behavior, showing (a) AC input power, (b) AC output power, and (c) inverter power, for all units. This was displayed via a node-red dashboard.
Normally the system operates fine, and all 4 units are inverting at the same “inverter power” (as expected when ESS is set to “total of all phases”). I’ve not yet verified whether the imbalance within a phase is “real” via a clamp meter (because I forgot to check) — but the readings above do seem to indicate both phases are inverting at different power levels, which is not the correct behavior (and leads to unexpected grid import/export).
To resolve this imbalance, we flip off the AC breakers to/from both slave units, let the system run for a bit with heavy load — so all power is flowing through the masters — and then flip the breakers back on (a “live” fix). Rebooting the units sometimes resolves it too. It’s somewhat inconsistent which of these two fixes it.
Some details on the system:
- Installed ~4 months ago
- 4x Quattro 10k 120v units, in a 2x2 split-phase configuration
- Firmware version v556
- Cerbo on latest beta or stable firmware (behavior happens on both)
- We followed the wiring unlimited manual very closely. All terminals were torqued within spec of the manual, identical wire lengths for units in parallel, of minimum gauge for our building code.
- Our dealer ordered a dedicated batch of 4 units for our install (serials indicate they were manufactured within 1 week of each other).
- 60kWh Discover AES battery bank with CAN-bus BMS
- Grid code set to “other”
- ESS grid setpoint of 0W, and multiphase regulation set to ‘total of all phases’
- All loads are on the output side of the units, with ESS using the Quattro’s internal meters
We’ve tried the following, which didn’t help:
- Flipping the master/slaves in software
- Changing grid input connection from AC In 2, to AC In 1
- Changing multiphase regulation to “individual phase”
- Restoring configuration to default, and rebuilding the settings
- Double checking the AC/DC connections are torqued and proper. For example, when this imbalanced behavior is occurring, we can switch to “inverter only” mode and everything will correctly operate in-balance in terms of AC Output and Inverter power. So this to me implies the AC output / DC connections are correct. This could still imply the AC input side is incorrect, though we’ve triple checked the torque on these (e.g., when switching from AC In 2 to AC In 1).
The fact that (a) the system can run stable for weeks at a time, and (b) a reboot / toggling a breaker resolves this implies to me there is probably a firmware issue somewhere (e.g., see this thread where someone else’s imbalance issues were resolved via a firmware update a couple years back).
I’ve asked my dealer for assistance, but would also appreciate the wisdom of the crowd here.