Hello,
A system consisting of:
- MultiPlus-II 3000 GX
- V-TAC battery 5kW
The system is used at the moment as test system / ups system.
No assistants installed.
Is configured to disconnect the grid after absorption finished and reconnect the grid when the SOC is 20%.
For that I am using the virtual switch function, as “dedicated ignore AC input”.
Charging bulk and float configured as 56.4V, 3.525V/cell.
DVCC disabled, no BMS control on DVCC.
Plain and simple as possible.
As seen in the pictures below, it connects the grid, it bulk charges and then enters absorption phase (which is 1 hour - minimum possible).
During absorption, at some point, before 1 hour absorption end - at about 45 minutes - the BMS says that it’s done and sends CCL = 0A.
In that moment the MP2 voltage spikes to 63V and switches OFF !!!
You will say - hey, the power doesn’t have where to go and therefore the spike…
Just take a look in the picture at the currents (MP2 and battery) in that moment… 0 (zero) Amps !!!
So the spike is NOT justified.
More than that, the OFF state is not justified !
No errors logged.
You will say: why not using DVCC?
Because all parameters can be set from the charger - current limit (18A), voltages (56.4V) and there is no need.
And still, I’ve also tried with DVCC enabled. The same !!
What happens???
It happened multiple times, so it’s repeatable…
If I try to turn it on from Remote Console, it spikes again and cycles: bulk → absorption → float → sustain (!!!) → off quickly.
Strange, huh ?!..