Overvoltage, Cerbo GX controlling SolarEdgePV, Sunspec: ‘Dynamic power limiting’ option not working

Hi there. I have nearly the same setup as yours. I managed to use the “Dynamic Power Limiting”. So far everything seems to work.

3x Victron MPII 5000
–> 12x Voltsmile V10 RPC & MPPT 250/100 (with 5,4 kwP)
—> SolarEdge 12.5K on AC-Out

I update my SE12.5K last week.
I had to reconfigure the Solaredge Modbus TCP Configuration (Chapter 5 from here: Integrating with SolarEdge [Victron Energy] ).
I also configured the frequency shifting & Solaredge APS switching wenn offgrid (described in aboves link)

Victron Config:

  • Switch for Solaredge APS wen offgrid (Assistent 1+2)
  • Go offgrid wenn input AUX1 is used (Assistend 3-5)

Import:

  • I used the the Victrons AUX Relais (NO + COM) to interconnect to Solaredge Communication Board (L1+V).
  • I also deleted the SolarEdge Smartmeter Config (i think you can also just deactivate the Smartmeter) & the restarted the Solaredge Inverter. (For some reason the dynamic power limiting didn’t work with the SE Modbus Smartmeter configured)

Last steps:

  • Restart the CerboGX
  • Configure the “dynamic power limiting” for SE

Hint: I didnt configure the SolarEdge inverter as “Modbus device” but used “Seeting > Integrations > PV Inverters” and also entered the SE inverters IP manually in the config, and didn’t use the “auto scan function”