On the cottage I hava an off-grid PV system consisting of: Multiplus II 24/3000, Smartshunt (connected with VE.Direct to Multiplus) and SmartSolar charger 100/20 (connected to Multiplus with VE.Direct USB cabel). The system includes 3 x 350W PV panels connected to the Multiplus, and to catch the morning sun, I have a 440W PV panel on the sauna building (named Bastu in the pics below) connected to the 100/20 SmartSolar charger. The battery bank consists of 4 x 220Ah AGM batteries.
Everything works well overall, but I’ve noticed two issues:
Even though the “Bastu” PV panel provides around 340W, the status still shows Idle or even Discharging.
Thanks @pwfarnell . You are absolutely correct. Negative goes directly to battery, not to the shunt. I did also read your post about the settings and I changed them accordingly. I will re-wire the negative next time I visit the cottage. Thank you one more time!!