Newbie. Recent install of Smart Shunt while the bank was fully charged, bank disconnected from both loads and the charger. I did not do a “manual sync” because it already reported SOC = 100%. Bank is now connected to loads. And remains not connected to charger.
Has been in use for 1/2 day. It’s current voltage of 24.73V (its a 24V system) clearly indicates that real world SOC is well below 100%. But the shunt is still reporting 100%. That’s my problem. What did I do wrong?
The bank is four Concord Lifeline AGMs in good condition (I think). Each 210Ah. Wired up as a 24V system. Shunt’s Capacity = 840Ah.
The charger is a Skylla-i 24/100(3) 230V. The naming of its charging phases is slightly different than typical. They are:
- Bulk = 28.4 V
- Absorption = 28.4 V
- Float = 27.4 V
- Storage = 26.4 V
I see the charger at 26.33 to 26.4 V when it switches to Storage (with a target of 26.4 V). I see this both from the Shunt’s logic as well as from a separate Murata digital multimeter connected to the same physical shunt.
I see the charger switch to Storage (26.4 V target) in the range of a few amps of current (don’t remember exactly), as reported by the shunt’s logic and the Murata (which reads amps high). It typically takes overnight to achieve that.
There are two of these banks, on a single buss, with the loads and charger attached to that single buss. 0, 1 or 2 banks attached to the buss at a given point. Typical charging routine is to fully charge bank X while on the buss, once charged swap banks putting Y on the buss, with X now fully disconnected, and resting.
Shunt’s Charged Voltage set to 26.3V. This is slightly below the voltage at the “point of full charge”.
Shunt’s Tail Current set to 1% based on the FAQ recommendation. However, I see the charger switches to Storage (26.4 V target) in the range of a few amps. So perhaps I should lower the Tail Current to 0.5%? But in either case this seems pretty close to the “point of full charge”. Advice on that?
Screenshots of status and settings attached.
The auxiliary input is setup for “temperature”. The retailer said that the shunt’s readings will flow to the Skylla-i. But there are 3 shunts in the system. How does the Skylla know which reading to use? Now that I’m more familiar with how this thing works, I’m in serious doubt about this flow of temp information.