Newbie here just getting into the Victron world. I have pieced together a new system for my RV and looking for input into my design before I start installing. It is all sitting in my garage right now, powered on with a couple of DC power supplies and connected via VRM and everything is update to date. Going to hook up the batteries and start final testing this week and hopefully install this weekend, weather permitting.
Here are the particulars:
Existing design:
2022 Riverstone Legacy 42FSKG fifth wheel
2x 100ah Go Power LFP
Go Power Weekender 570w solar package (3x190w panels parallel, 30-amp PWM non-bt SCC)
Go Power 1500w inverter with Transfer Switch
PD-9380v converter/charger
WFCO 8930/50 PDC (not split phase, just 120v x 2 design)
Firefly Integrations system running house, hvac, water pumps, etc.
Onan 5500 LP generator
WFCO T-57r ATS
Progressive EMS50-HW power protection on shore power input
What I have bought:
Multiplus II 12v/3000va/2x120v
MPPT 100/50 SCC
Lynx Power In, Shunt, Distributor
Cerbo GX MK2
1-off-2 Manual Transfer Switch
2x Wattcycle 12v 314ah Smart Minis, each one into Power In separately
Several breakers, cabling, lugs, etc. needed
What I am removing and changing:
Remove PD-9380v converter
Remove Go Power Inverter
Remove Go Power SCC
Remove Gp Power 100ah batteries
Convert solar panels from 3P to 3S configuration
I have attached a rough diagram showing the desired build. I have some other things that I will seek input on, but my primary concern is the basic system diagram right now. I am installed a manual transfer switch so that I can bypass the MP2 if needed while on shore power or generator. It will fed by the ATS output on input 1, middle position is off, and from the MP2 AC out 1 into input 2 (primary position). My RV disconnect switch feeds the PDC and the firefly system (4 wires into the disconnect switch) and I will be leaving that as well as the non-switched loads like the hydraulic pumps for levels & slides and the disc brakes, generator start circuit, safety equipment in place mostly as is for now. I will leave the inverter in place for now but disconnect it from all power. I will pull the 20amp AC breaker that feeds the converter out and replace with a 15 amp breaker and connect the inverter fed circuit from the new 15amp breaker. With my original inverter only certain outlets and the residential fridge ran from the inverter, but now the whole trailer could run from the batteries now up to the MP2 output limit.
All of the wiring I have is labeled on the diagram and is 105 degree C welding cable. Each battery connects to the Lynx Power In via 350amp class T fuse and 250amp breaker/disconnect via 2/0AWG. The MP2 connects to the Lynx Distributor with a 400amp MEGA fuse via 4/0 AWG. The Lynx Shunt has a 500amp MEGA fuse installed and is the main breaker for my system. The Distributor will be grounded to the RV frame via 4/0AWG to a new ground location with 3/8” zinc bolt tapped into the frame directly. I will also connect the always on DC loads, the generator start circuit, and the MPPT 100/50 SCC to the Distributor, so it will be full.
I feel like that is a wall of text, but I am very appreciative if anyone can help me debug the logic and make sure it all makes sense. I am happy to include more details if it is helpful, but I think the diagram has most of it now. Thanks for reading and looking!
In the diagram, the reddish arrows note AC power, white is DC.