We stopped using the Norcold (1200 LRIM) on gas when we saw how many units it burned down. We missed out on the class-action lawsuit though
which was a shame because it would have paid for the new residential fridge, as it did for so many others. Lots of videos of Monaco’s on fire from this, and I talked to one fella that went through it, and to this day, he cannot enter someone else’s RV if it has a Norcold in it. He’s that emotionally scarred from it because it burnt up so fast he could only get one shoe on
and lost everything as it was his home.
I ordered up the 120x2 as well as the USB programming interface so the project is a go
I will start with just replicating the existing 30A inverter setup for expediency, and then upgrade to the 50A feed thereafter. That’s what I am looking into now.
If you have time, feel free to comment, but if I’ve taken up too much already, feel free to ignore me
Some other kind soul will likely help or I’ll figure it out myself as I go along. I’m trying to break it down into simple steps for clarity, work flow & sourcing/purchasing purposes.
This is what the OE wiring looks like with respect to the incoming 15/30/50A feed;
A) The panel appears to be fed 50A (120x2) directly from the transfer switch. Those wires (Red, Black, Green & White) currently go to a 50A breaker in the box providing full 50A power, if available, from either the pedestal or generator. (see second pic top right and bottom breaker)
This line should be replaced with #6/4 SOOW and run from the transfer switch to AC IN on the inverter, which would provide the full source power, including 120x2, to the inverter from either shore or generator.
B) OUTPUT 1 on the inverter should be #6/4 SOOW and run to the 50A breaker (bottom) just as it is now, with each leg on it’s own side of the breaker.
In this scenario, when supplied with reliable power, whether it’s 15, 30 or 50A, it will passthrough the inverter, to the breaker box, just as it does now. The only difference is that the electrons take a longer route to get there by going through the inverter.
If plugged into a 15A pedestal, as an example, and the inverter is set to 13A, and you draw 20A, then the inverter will add ~5A from battery power to make up the difference for as long as the load is present, or your batteries can hold up.
So the only difference from OE design to passing the the source power through the inverter first is that this makes the inverter a single point of failure.
If this is correct, I am unsure why you replaced your panel. According to Victron specs the max peak power the inverter can put out is 5500W or 45.83A That should be acceptably below the threshold of the 50A feed breaker.
I believe the loads in my breaker box are divided up such that L1 powers some, and L2 powers some. This is probably done to ensure things like the two AC units use their own leg and other, less load drawing devices share the other leg. Ie, for capacity reasons.
If the 50A feed breaker in the panel is wired the same way, and fed from the inverter instead of the transfer switch, then in a passthrough situation (15/30/50) nothing has really changed other than the power is passing through the inverter.
When on battery power, what has changed is that the inverter now powers the entire panel, and not just some outlets.
If I’m in error on any of this, please let me know.
One issue that comes to mind is this, the existing inverter has two 15A circuit breakers on it. Those breakers, and the inverter, appear to feed the inverter output outlets in the vehicle. As such, I doubt they go to the panel at all. In effect, it seems to me that the inverter with it’s two breakers acts as a panel. I could be wrong on that…but it seems like this would have to be dealt with, otherwise all of those outlets would not be fed power.
Update: It looks like AC-Out-2, which is normally turned off in the event that unit goes to inverter/battery power, can be configured with VEConfigure to be kept active based on battery voltage. Ie, if the battery voltage is >10v, AC-Out-2 is kept active regardless of whether the unit is inverting or not.
So that should solve the immediate issue of what to do with the 2 output circuits going to the old inverter.