so I’m troubleshooting an off grid system with a Genset .
The installer has the ground relay active and when victron is the power source there’s near Zero neutral to ground voltage .
He did NOT bond the neutral to ground at the 3 phase diesel generator ,which resulted in a floating neutral .15 volts neutral to ground difference.
I corrected it and bonded the neutral at the to the ground at the generator , but when the Genset is running the ground to neutral voltage is reduced ,but it’s still 3 volts at the main panel in the home and the sub panels .
at the generator and generator transfer switch panel it’s near Zero .
Any ideas ?