I saw an install today , 3 phase off grid multiplus 2 . The victron distributor /installer only connected one of the 3 multis to ground via ac in ,(Genset )
All are connected to ground on ac out ., which I realize is the same grounding bar that the ac in ground connects to
The effort required to connect the other two would be very low. These should already be integrated.
Depending on the supply line, a PE is also connected.
Since the supply lines also carry a PE, nothing will happen for the time being.
If no PE is connected to the supply line, the AC In relay test will not work and the network of the 3 MP will not be able to switch to the mains.
The earth is required on all of them to enable the filters to operate. Further, the case potential will rise to half mains potential. A typically non lethal level, but if the case is touched you will get a tingling sensation.
Is that an inline joint in the trunking wrapping in tape?