Need feback on setup for Quattro II setup with two US5000 in Sweden
Just looking for some feedback to verify the setting. (Have not set this myself)
AC 2 in is generator.
Can you explain the LOM?
Best,
Andreas
TAB: General
System frequency 50Hz
Shore current 25.0 A
Overruled by remote unchecked
Secondary input shore current 10.0 A
Dynamic current limiter unchecked
State of charge when Bulk finished 95.0 %
Battery capacity 200 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard Denmark: DK2, Eastern Denmark (Technical regulation 3.3.1)
AC input 1 Above selected gridcode, no LOM detection (compliant)
AC input 2 Above selected gridcode, no LOM detection (compliant)
TAB: DK2 (Eastern Denmark)
Use AUX1 as disable FeedIn signal checked
Maximum AC current for charge or feed in 80.0 %
Maximum generated apparant power 100.0 %
connect waiting time 180 s
connect power ramp 300.0 seconds
low frequency connect value 49.900 Hz
high frequency connect value 50.100 Hz
low voltage connect value 85.00 % Un
high voltage connect value 110.00 % Un
re-connect waiting time 180 s
re-connect power ramp 300.0 seconds
low frequency re-connect value 49.900 Hz
high frequency re-connect value 50.100 Hz
low voltage re-connect value 85.00 % Un
high voltage re-connect value 110.00 % Un
rise-in-voltage protection U> 130.00 % Un
under voltage stage 1 85.00 % Un
under voltage stage 1 delay 50.00 s
over voltage stage 1 110.00 % Un
over voltage stage 1 delay 60.00 s
under frequency stage 1 47.500 Hz
under frequency stage 1 delay 0.20 s
over frequency stage 1 51.500 Hz
over frequency stage 1 delay 0.20 s
under voltage stage 2 80.00 % Un
under voltage stage 2 delay 0.20 s
over voltage stage 2 115.00 % Un
over voltage stage 2 delay 0.20 s
under frequency stage 2 46.000 Hz
under frequency stage 2 delay 0.00 s
over frequency stage 2 54.000 Hz
over frequency stage 2 delay 0.00 s
P(f>) start frequency 50.500 Hz
P(f>) stop frequency 50.500 Hz
P(f>) start delay 0.50 s
P(f>) stop delay 5.00 s
P(f>) droop 4.00 %
P(f<) start frequency 45.000 Hz
P(f<) stop frequency 45.000 Hz
P(f<) start delay 0.00 s
P(f<) stop delay 30.00 s
P(f<) droop 4.00 %
P(U) response Not used
Reactive power regulation Use a fixed Cos Phi
Filter time for reactive power 3.3 s
Cos phi 1.00
Use lock-in/out checked
Lock-in voltage 105.00 % of Un
Lock-out voltage 100.00 % of Un
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
Inverter DC shut-down voltage 43.50 V
Inverter DC restart voltage 44.50 V
Low DC alarm level 44.00 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Disable VSense (for diagnostic purposes) unchecked
Configured for VE.Bus BMS unchecked
Charge curve Fixed
Absorption voltage 53.50 V
Float voltage 53.00 V
Charge current 20 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
programmable relay (size:176)
*) Use ACOut 2 relay.
*) Set relay off
*) when Auxiliary input 2 is open for 1 seconds.
programmable relay (1) (size:37)
*) Set relay on
*) when Auxiliary input 2 is closed for 1 seconds.
ESS (Energy Storage System) (size:1033)
*) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus or a BMS system in which the
batteries are protected from high/low cell voltages by external equipment.)
*) The battery capacity of the system is 200 Ah.
*) Sustain voltage 50.00 V.
*) Cut off voltage for a discharge current of:
0.005 C= 44.60 V
0.25 C= 44.40 V
0.7 C= 44.30 V
2 C= 44.20 V
*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).
*) Relevant VEConfigure settings:
- Battery capacity 200 Ah.
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
Total size of all assistants including the required
(hidden) system assistants is: 1320
TAB: Advanced
limit internal charger to prioritize other energy sources unchecked
LOM means loss of mains - ie when Grid fails.
Thanx, just need to know if it has to be enabled here in Sweden.