I have a 3 phase system with 3 times multiplus 2 type 48volts 4k5.
It has run on AGM batteries before without problems. I have now installed a new 48volt battery with Sodium ion cells and I can’t get it working. As soon as I connect the ve bus to the cerbo it shuts down.
In have exchanged the rj45 cables for new ones and have one cable to the cerbo modified for pin 7
Still the same problem. Software version is all updated to the newest versions on GX (3.70) and Multiplus(557).
Hello Marc, thanks for asking. My system consists of 3 Multiplus-2 units in a 3-phase configuration.
It is connected to a 16 cell sodium ion battery with a standalone JK-BMS. Yes the output voltage from the battery is high compared to a Li-ion battery, but is quite normal for a Sodium cell battery. In the beginning when the cells were not fully charged, about 48 Volts, the behavior was the same.
The battery is wired via a DC-Bus to a Victron MPPT 450/100.
The Cerbo GX is also directly connected to the DC-bus.
I will send you some pictures of my system later today.
Hello Nick, thanks for your support. I have read some threads on this subject so I dubbel checked. I am sure I have connected the first of the daisy chained MP2 to the VEbus socket. These are located underneath the Ethernet socket.
Yes, as soon as I disconnect the VEbus connection, the MP2 starts.
What I think is strange is that when I connect my MPPT450/100 it is not visible in the GX configuration. It is visible local via bluetooth.
Problem solved by replacing Cerbo GX. I have ordered a new Cerbo GX and now the system is behaving normal. The only thing I do not understand is why I do not see my MPPT450/100 in VRM. Could it be that the VE-bus of the MPPT is also gone defective?