Can someone have a look at these settings and advise if they are right.
It’s bulk charging at the moment and never goes into absorbtion. The bulk charge voltage should be 28.8 but I don’t know how to set it.
It’s charging at 56A; should it not charge at 70?
The generator is sending 238V to the Multiplus. Should that be 230V
Voltage regulator might be a hair high on the generator but nothing to be concerned about
As for the charge current, do you happen to have an input current limit set? By the looks of that screenshot I would almost suspect maybe the input current limit is set to 10a.
Another thing to try is checking the “weak a/c input”, I know with my unit if I start loading up the generator too much with the multiplus charger it would start doing weird things without that box selected.