These are the settings.
Settings Summary
TAB: General
System frequency 50Hz
Shore current 50.0 A
Overruled by remote checked
Dynamic current limiter checked
State of charge when Bulk finished 98.0 %
Battery capacity 800 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard None: (feeding energy from DC to grid not allowed)
Accept wide input frequency range (45-65 Hz) checked
AC low switch mains off 180 V
AC low switch mains on 187 V
AC high switch mains on 265 V
AC high switch mains off 270 V
UPS function unchecked
TAB: Inverter
PowerAssist checked
Assist current boost factor 2.0
Inverter output voltage 240 V
Ground relay checked
Inverter DC shut-down voltage 22.00 V
Inverter DC restart voltage 24.00 V
Low DC alarm level 24.50 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input checked
Stop after excessive bulk unchecked
Lithium batteries checked
Charge curve Fixed
Absorption voltage 28.40 V
Float voltage 27.50 V
Charge current 120 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
Assistants not used
Here is a screenshot of the Charger settings.
I am used to it derating (presumably to IGBT max temp) to about 95-100 Amps after a while. But now , even if the system was off, it will never go above 70. Usually it stays at 65/66 Amps.
Ambient Temp is 28C… Temp of Air out of top of inverter is 35-40C.
Firmware version is 481.
The inverter is connected to a Venus GX with VE Bus.
DVCC is not enabled.
Should I enable DVCC ? I have not, since not all devices are supported .
AC Power source is a 5.5kW generator.