MultiPlus II operate with two 230V phases without a neutral?

Hi, I want to install a MultiPlus II in a setup where Enphase microinverters are already present. However, this installation operates on a 230V two-phase system (single-phase 230V, 120° phase shift). The electrical grid is three-phase at 230V, so there is no neutral in the installation.

This raises my question: Can the Victron MultiPlus II operate with two 230V phases without a neutral? Thanks

Hi i think they do that in belgium too on a 230v delta network

So is possible

I understand that ‘So is possible’ is an affirmation? The doubt is that in Enphase’s documentation (image), it is indicated that the ground must be connected to the neutral, and also in the Miltiplus manual, it says ‘Do not invert the neutral and phase when connecting the AC power supply,’ and that when a grid power outage occurs, the neutral is connected to the ground through a relay (I think this can be programmed…). Thanks again

Yes that can be programmed, you could contact a belgium offical victron dealer that may give you some more info about this