Dear SvenW,

I’m seeing very similar behaviour on my 3-phase system after updating to GX v3.66 and Multi firmware 510.

In my case L2 and L3 remain in import / pass-through even though voltages, CTs, Dynamic Cut-Off, Assistants and the Pylontech US3000C BMS are all correct.
The system shows no VE.Bus error, and the behaviour is stable until I remove all Assistants — then everything works normally again.
Once the Assistants are added back, L2/L3 go into import again.

My second installation, with the same hardware and the same Assistant setup, but still running firmware 502, works perfectly — so the issue may be related to the newer firmware or ESS logic, similar to what you described.

I will reconfigure everything from scratch and also check VE.Bus configuration with MK3 next week.
Would be great to hear if you observe the same behaviour on GX 3.66.