Multiplus II 48/[5000|8000] Transformer Noise from Grid
Hello Victron community and developers,
I’m living in Ukraine, and as you know, we have a lack of electricity due to the war.
My two neighbors and I chose Victron Multiplus II 48/[5000GX|8000 Cerbo GX] inverters + DIY 280Ah batteries (16S) with JK BMS as ESS (without any PV systems yet). We live in private houses with a 3-phase (230V/400V) grid connection and use a single inverter (1 phase) only for critical loads. All three houses are connected to the same transformer substation, and most houses in that area use heaters, water pumps, water heaters, electric stoves, ovens, etc.
All systems were installed and configured similarly, and we faced the same Victron transformer noise issue. The noise is like pulsation, transformer vibration, or sinusoidal hum.
During a discussion about this issue in the Ukrainian Victron community Telegram channel, one of the installers suggested that the hum noise is generated by the Victron transformer due to high voltage/current harmonics in the grid.
We conducted a grid quality check using a Cesinel ReCon T electric power series logger device and obtained metrics/results. The auto-generated reports showed no critical grid issues, and all tests passed.
During troubleshooting, we found that:
- The hum noise occurs only when the grid is enabled, regardless of whether there are consumers or not.
- The inverter power consumption fluctuates (20–180 Watts) with the grid enabled and without consumers.
- There is no hum noise when we use a power generator as the “grid” input, with or without consumers.
- No hum noise occurs during inverter operation from the battery, with or without consumers.
- No hum noise was observed at another location. One of the Victron Multiplus II 48/5000 GX inverter was connected to the grid in an apartment (different transformer substation).
- Enabling, disabling, or changing grid codes (EN50549-1:2019; Other; None; with and without LOM), UPS function, Weak AC input, or ESS Assistant in the Victron inverter configuration had no effect.
- No installation or Victron hardware issues were found. These were checked multiple times by the community and professional installers.
- Installing a voltage stabilizer with transformer topology before the Victron inverter has no effect.
- The sine wave of each phase was checked with an oscilloscope and appears to have no distortions.
We still suspect this is a voltage/current harmonics issue. Is it possible to reduce or eliminate this hum noise by changing some grid parameters in the Victron configuration? Or by installing some device before the Victron inverter?
P.S. Four other neighbors have 3-phase Deye hybrid inverters (SUN-12K-SG04LP3-EU) with Non-Isolated/Transformerless topology, and they do not experience any grid hum noise issues.
P.s.s. Video files with hum noise and Cesinel ReCon T repors - Inverter_hum_noise - Google Drive
Thanks in advance