MultiPlus-II 48/10000 AC input current seems limited to ~30–32 A despite higher limit setting

Hello everyone,

I am currently testing a 3-phase system with three Victron MultiPlus-II 48/10000/140-100 units connected to an external AC source.

System setup:

  • 3 × MultiPlus-II 48/10000/140-100 (configured as a 3-phase system)

  • Controlled via Cerbo GX

  • External supply: 3-phase CEE 32 A

  • Cable length from distribution to system: approx. 30 m (5 × 6 mm²)

  • AC Input Current Limit set to about 33–35 A

  • Power of every MultiPlus set to about +7500 W

Goal:
I would like to reach roughly 22 kW total AC input power (≈7.5 kW per phase).

During testing I measured the following values at high load:

MultiPlus 1

  • U = 221.46 V

  • I = 30.38 A

  • P ≈ 6.70 kW

MultiPlus 2

  • U = 222.13 V

  • I = 31.17 A

  • P ≈ 6.88 kW

MultiPlus 3

  • U = 223.61 V

  • I = 29.33 A

  • P ≈ 6.52 kW

This results in roughly 20–21.5 kW total power.

At low load the voltage is around 228 V, but under high load it drops to around 222–223 V, which I assume is mainly due to the 30 m cable.

However, even when increasing the AC Input Current Limit on the Cerbo GX, the current per inverter seems to stay around 30–31 A and never approaches the configured limit.

I also verified that battery charge current is not limiting, since during the test a large AC load was connected and the batteries were not being charged significantly.

My question:
Is there an internal limitation in the MultiPlus-II 48/10000 that effectively limits AC input current to around 30–32 A per unit, or is the behavior simply caused by voltage drop and normal control margin?

Or are there additional settings that might limit the AC input power in this scenario?

Thanks in advance for any insights.

The Mutiplus has a 140 Amp charger

P = 140 x 48 Volt = 6.72 kW (15S)

Have you a 15S or 16S battery

1 Like

May need to clarify..
Its either not limiting charge or its not being charged significantly cant be both.

I am going to assume you have the ess assistant loaded since it sounds like you are limiting the ac output of the inverter?

What is the power factor of your load?
Are you using a grid code?

If you see 21kW at 222V - it’s ok.

In case 230V, it will be 22kW+

235V - 23kW+

I can’t understand what is “AC Input Current Limit set to about 33–35 A”

32A C class electrical circuit breaker can operate at 35A without any issues, if you have C32 (not B32!) you can try setup input limit to 35A

Also Cable 30m with 10 mm² per phase will be better for your target results

15S LiFePO4 have median voltage 50V

140A x 50V = 7kW DC

+2-4%% to transfer from AC to DC

in case 92% SoC at 3,55V per cell it will be 53,25V or ~7,5kW AC

Thanks for your reply.

The battery should not be the limiting factor in this case. I am using 5×6 Pylontech US5000 modules, so there is more than enough battery capacity and charge capability available.

During the test I also had several large AC loads connected, so the power coming from the grid was not mainly used for charging the batteries, but was largely consumed directly by the AC loads.

Because of this, the 140 A charger limit of the MultiPlus should not be the bottleneck in this scenario.

1 Like

Thanks for your input.

Unfortunately I cannot change the cable cross section in this installation. With the relatively long cable (about 30 m, 5×6 mm²) and currents around 30 A per phase, a voltage drop is expected, which then also reduces the achievable power. So seeing around 222–223 V under load makes sense.

Regarding my statement “AC Input Current Limit set to about 33–35 A”: what I meant is that the AC input current limit configured on the Cerbo GX was set higher than 32 A, sometimes even up to 37 A during testing.

However, even with this higher limit configured, the current per phase never exceeds roughly 30–32 A. That is why I was wondering if there might be an internal limitation per MultiPlus unit or if this behaviour is simply the result of voltage drop and normal control margins.

1 Like

What grid code are you using? Try test with “other”.

1 Like

Hi Hendrik, thanks for your explanation, and I really like it!!

About grid code, my opinion YES, it can help you to achieve your goal.

From my experience (not from documentation!) Victron hardware and firmware works with AC input through grid codes algorithm in very standard way, which is:

If AC voltage drops to undervoltage value, Victron trying to reduce AC power just to keep this voltage value.

If this value is 218 for example, Victron will try to keep it in 217-219V by reducing amperage from AC input.

It have 16S LFP configuration

Charge voltage 52.5 ~ 53.5V

In case 1% SoC it have minimum 46,4V in idle state, but if it starts to charge, voltage significantly increases to ~49V, it’s ok and it can tell us

When we start 140A charging 1% SoC batteries we can see 6,8kW DC charging or 6,9kW on AC input (without additional AC loads)

In 10 minutes it can be 7kW AC input, in 30 minutes ~7,2kW

? I think it is a 15S

1 Like

I think you can use from AC more than 32A in case AC charging plus aux AC loads

My bad, sorry 15S

This is my 15s LFP 600Ah real data around 30-100%%, we can see voltages at 0,1C charging current