I am investigating repeatable “Low battery” trips on a MultiPlus-II 24/3000/70-32 and would appreciate clarification on the protection behaviour.
System Details
-
Inverter/charger: MultiPlus-II 24/3000/70-32
-
Battery bank: 4 × Leoch LDC6-400-L16 AGM (6 V, 400 Ah each) in series
-
24 V nominal
-
400 Ah total capacity
-
-
Battery monitor: SmartShunt 500 A (all battery current passes through shunt)
-
Temperature: ~8 °C in battery room
-
DC cabling: Short runs, 125 A DC fuse, connections checked tight
-
No grid interaction during test (inverter-only island mode)
Relevant VE.Configure Settings
-
DC input low shut-down: 18.6 V
-
DC input low restart: 21.8 V
-
DC input low pre-alarm: 21.8 V
-
Charger absorption: 28.8 V
-
Float: 27.6 V
-
Charge current limit: 70 A
No Assistants beyond standard ESS. Scheduled charge disabled during tests.
Observed Behaviour
During inverter-only testing (AC-in disconnected):
Case 1 – ~1350 VA load
-
AC output: ~1352 VA
-
DC current: ~−62 A
-
DC voltage (VE.Bus): ~23.6 V
-
Udc ripple: ~0.5 V
→ MultiPlus asserts “Low battery” alarm and trips.
Case 2 – ~1950 VA load
-
AC output: ~1959 VA
-
DC current: ~−94 A
-
DC voltage (VE.Bus): ~23.0 V
-
Udc ripple: ~0.6 V
→ Also trips “Low battery”.
In both cases:
-
Measured voltage at MultiPlus DC studs with DMM matches VE.Bus reading (~24.7 V at rest, ~23.6–23.0 V under load).
-
Per-battery measurements under ~1250 W load show balanced sag (~5.93 V per 6 V block).
-
No significant voltage drop across fuse or isolator.
-
SmartShunt minimum voltage does not show values anywhere near 21 V.
Given the configured shutdown of 18.6 V, and restart 21.8 V, the observed trips at ~23–23.6 V appear inconsistent with the static thresholds.
Questions
-
Is there a dynamic low-voltage protection curve in the MultiPlus-II firmware that trips above the configured static shutdown voltage at certain current levels?
-
Is there a separate VE.Bus low battery alarm threshold (distinct from the Inverter tab “DC input low shut-down”) that could be active?
-
Does the firmware implement a current-dependent protection mechanism that could trip around ~23 V at ~60–90 A discharge on a 24 V unit?
-
Are there any known issues or firmware revisions addressing premature low-battery trips on 24 V MultiPlus-II systems with AGM batteries?
-
Is there any additional diagnostic logging available to capture sub-second DC voltage dips not visible in the VE.Bus monitor display?
Additional Context
-
Batteries are ~2 years old AGM.
-
Balanced under load.
-
Temperature ~8 °C (cold but not extreme).
-
System is stable below ~1.0–1.2 kW but trips above that level.
Before redesigning the system around lower discharge limits, I would like to confirm whether this behaviour is expected firmware protection or indicative of a configuration or hardware issue.