A bit stumped by this error showing up in the startup of this system. Further details:
3x Multi RS Solar 48/6000/100 - 450/100 firmware v1.31 product ID A443
Three-phase net configuration
ESS in-line with net to home (domestic installation)
DC bus with power-in, lynx shunt VE.can and Lynx Distributor
Cerbo GX MK3
What we’ve tested so far:
When the system is connected to the grid, it will start up and close AC relays just fine, effectively running in pass-through mode. So far, so good. Note that DC bus is also up and running, batteries are connected, but powered off! (3rd party batteries running off their own BMS).
Next, we powered down the grid connection, and powered up the DC bus by powering on the batteries. This will also start up just fine, and the inverters go into inverting mode. AC output is generated and measured on the AC out’s of the inverters. Again, so far so good.
Finally, we also reconnect the grid on AC-in. The inverters will recognize this and start counting down 60 seconds before they close the AC relays. Once counted down, the AC relays will close and after about 2 or 3 seconds, they will disconnect again.
Error message on Cerbo and displays is PV2 Error : Isolation Failure
Fun fact; the is NO PV connected to either of the MPPT inputs at all. The DC switch is OFF. And in the VictronConnect configuration, we have turned OFF Solar MPPT inverters.
As soon as we disconnect the grid input from AC-in, again the inverters will succesfully close the AC relays and go into inverting mode.
Any suggestions as to what could be contributing to this PV2 Error: Isolation Failure? There’s no PV connected at all, and furthermore it’s fully disabled. So this error seems to be a false reading. But as to now we’re stumped as to what could be causing this error.