Multi RS Solar 48/6000/100-450/100 PV Isolation failure with no PV connected

A bit stumped by this error showing up in the startup of this system. Further details:

3x Multi RS Solar 48/6000/100 - 450/100 firmware v1.31 product ID A443
Three-phase net configuration
ESS in-line with net to home (domestic installation)
DC bus with power-in, lynx shunt VE.can and Lynx Distributor
Cerbo GX MK3

What we’ve tested so far:
When the system is connected to the grid, it will start up and close AC relays just fine, effectively running in pass-through mode. So far, so good. Note that DC bus is also up and running, batteries are connected, but powered off! (3rd party batteries running off their own BMS).

Next, we powered down the grid connection, and powered up the DC bus by powering on the batteries. This will also start up just fine, and the inverters go into inverting mode. AC output is generated and measured on the AC out’s of the inverters. Again, so far so good.

Finally, we also reconnect the grid on AC-in. The inverters will recognize this and start counting down 60 seconds before they close the AC relays. Once counted down, the AC relays will close and after about 2 or 3 seconds, they will disconnect again.
Error message on Cerbo and displays is PV2 Error : Isolation Failure

Fun fact; the is NO PV connected to either of the MPPT inputs at all. The DC switch is OFF. And in the VictronConnect configuration, we have turned OFF Solar MPPT inverters.

As soon as we disconnect the grid input from AC-in, again the inverters will succesfully close the AC relays and go into inverting mode.

Any suggestions as to what could be contributing to this PV2 Error: Isolation Failure? There’s no PV connected at all, and furthermore it’s fully disabled. So this error seems to be a false reading. But as to now we’re stumped as to what could be causing this error.

I’m taking this literally: could it be that your DC isolation switch or breaker is broken? Did you actually try to remove physically the PV wires from the charger input terminals? If you do that, be careful not to cause a short.

Interesting take, for sure… It does make me realize that we’ve not taken a close look at the source of the PV2 Isolation Fault message. Is it present on all 3 inverters, or just on one? If it’s only present on one, it could well be a fault within that single Multi RS Solar…
But still odd that the issue isn’t there when operating only on DC, no grid connected. Neither is it present when grid is connected, but no DC is present. So I have a hard time accepting that it would be related to PV at all… Still one to check, though! Thanks.

What types of switches are in use? There are various types of PV switches.

Check the non-resettable safety relays at the PV input. They have a little red flag on them.

I had one with activated relays out the box, never had PV connected.

RMA did replace the unit for free.

I’m having similar issues. I get intermittently an “Error Code: #42 - Inverter shutdown (ground current too high: >30mA)”. causing everything to shut down. It also happened when there was no PV attached to that MultiRS.

The Multi RS Solar comes with built-in DC disconnect switches. I don’t have a brand name or type on them, but will have a look and update once I know.

Any chance you have a photo or more details as to where these safety relays sit on the board? I’m having a hard time locating them exactly (or not sure what I’m looking at, other than the onboard DC fuses)