Check grid voltage and frequency. If it started to happen out of a sudden and behaves the same for two different units, then it is very possible that the grid may have issues.
Any (new) construction sites or something similiar nearby? Sometimes big machinery without or with damaged “soft-start” can pull grid voltage down. Multiple times a day, everytime causing the multi to disconnect, but reconnect again quickly as that “drop” just lasts couple of (milli-)seconds.
When checking VRM advanced, it may even be tricky to see, as these graphs only have a 1-min resolution.
I agree, should be one click right?, il looked at the detailed VRM logfile this morning , voltage 231Vac max and 222Vac min. Frequency’s between 50,3 and 44.9 Hz
Last night ac1 remained connected, until the sun came up, logfile showed thirty times a Ac1 disconnect state over a period of three hours
My solar is ac in connected, Enphase micro inverters MQ8MC ,could they cause the ac1 to open ?
Depending on your grid code, the voltage might be ok, but the lower frequency of just 44.9Hz is very likely too low, so the mains gets rejected based on low frequency.
In VictronConnect, under Settings and Grid, you can see the gridcode that is set but also further down the NS protection log, in that it should say why the MultiRS disconnected from the grid