Hi looks like everything is back to normal ![]()
I quickly want to explain, why the cause of this behavior, was not obvious or easy to spot - at least not for me:-(
In my system configuration the Quattro’s inputs are connected and configured:
AC1 = Generator
AC2 = Grid
As I wrote in another Topic, Quattro & BYD V2L - Grid Feed-in Problem
I sometimes have a car with:
V2L connected to AC1.
To prevent the solar battery being charged from the cars battery,
I had to install an assistant: “charge current control” see above pic.
This assistant was set as in the pic above, but with 1 addition:
I also had the option “Disable charger when charge current should be zero” ticked.
What was not obvious, is that this also has an effect on the MPPT’s ,
when ONLY AC2 is connected!!
Luckily Nick & Izak Burger, who seems to have has some insight of the inner workings of the assistant, gave the right hint ![]()
THANK YOU
Cheers and thanks to all participant, for your inputs and help ![]()
Jurgen from Namibia
PS: I never thought about the assistant, causing this - shame on me ![]()