I want to share my experience with the Lynx Class-T Power In, because I think this is a safety issue other installers should be aware of.
The problem
On my units (S/N HQ2610YUZEF and HQ2610RRUM9), the busbars were not aligned with the adjacent Lynx modules. Connecting them put the busbars under mechanical stress. In addition, one side of the Class-T fuse seat sat about 2 mm higher than the other (and angled). Torquing the fuse nuts to spec would force the fuse body to bridge that difference, with a real risk of cracking the ceramic fuse housing. A cracked Class-T fuse in a lithium battery bank is exactly the failure this product exists to prevent.
The process
It took about 2 months via Top Systems (NL) before the defect was acknowledged by Victron. Today I received my two ‘modified’ units. I was told they had been corrected, but noticed the housing had been heated and then deformed to compensate for the misalignment.
Result
The modified units are still out of alignment. Measured with a steel rule across both fuse contacts: about 1.5mm height difference (photos attached). Apart from not solving the problem, I don’t consider a heat-deformed plastic housing an acceptable fix for a component carrying 250 A / up to 1000 A on the busbar.
System context
Fixed home installation: 3× MultiPlus-II (3-phase), Lynx Smart BMS, 16 LFP modules in 4 strings, Class-T 250 A per string.
Questions for Victron
Is this a known production issue, and which serial numbers or batches are affected?
What is the actual tolerance specification for the fuse seat height?
Is heating and reshaping the housing an officially approved repair method?
What is the proper solution: a correctly manufactured unit or a refund?
To other users: please check your Class-T Power In with a straightedge before torquing the fuses.