Low battery notification while it does not appear low

Hi,

I am getting alarm low battery voltage, which then stops the operation.

When I check the battery it’s voltage does not appear to be low or discharged to a level that is alarming.


The alarms comming from the BMS are all OK



I also checked VE.Configure for the voltage values which are in alignment with the battery manufacturer.




Manufacturers manual for reference.
FLA48500-Manual (2).pdf (4.1 MB)
Update:

Appears to happen at 51.75v

What is causing the alarms? Is it an actual short voltage sag? Or more a configuration I am missing?

Thanks!

Voltage drop between batteries and multiplus

Fixed by implementing the solution on this post :

Just as a sidenode, the official documentation about using Pylontech batteries states to set these values to 46V.

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

Dynamic cut-off values: set all values to 46V.

1 Like