Loud humming noise and voltage fluctuations

I am sorry but you are missing the point entirely…

One last time…

The grid is huge and in this context, its voltage and frequency can not be influenced, significantly, by anything any appliance or equipment you have can do to it.
Unless the fault is so huge that it is taking out breakers or fuses.

I am not suggesting that the Inverter isn’t causing the voltage swings you are seeing, wherever you are measuring them, clearly it is.
I am saying that concluding it is faulty is not sound reasoning, because it would have to be drawing hundreds of amps, possibly many hundreds, depending on where you are measuring it, for it to affect the voltage that way. Assuming everything else is OK

It is just as likely that you have an issue elsewhere that makes relatively small load changes pull the voltage down, again wherever you are measuring it, and that this is causing the inverter to behave the way it is…

If you plugged a microwave into a long skinny extension and found that it reset itself every time you pressed start, would that mean that the microwave was faulty? or that way it was being used was inappropriate?

You will not fix your issue by taking one reading and jumping tom a conclusion.
You need to work through the problem and find where the voltage drop mis and how much load is required to cause that much voltage drop, as I have previously described…

With the inverter off…
If you can attach a 4kW load, circa 16 A at 240V, at the point where the inverter is connected to the supply, and you don’t see a voltage drop, then it would be reasonable to conclude that the inverter is somehow drawing massive current and is in fact faulty.
If your test load produces any significant voltage drop, which it absolutely shouldn’t, then you are looking for a fault somewhere else within your installation.

I do not know how to be any mire clear.
If you don’t test, logically, you will not find the issue.

Honestly, you may be better calling an electrician as you don’t seem to be grasping the problem.
I don’t mean any offence and I realise this could be a language thing, however it feels like you not understanding the problem, as opposed to not understanding the words.

If you don’t understand what I am asking you to test, or why, please get someone qualified to do the testing as that will be safer and more effective.

I can’t help any further until you, or an electrician, gathers more information.
be careful,
I hope you pin down the issue.

NB.
To be 100% clear here…
If I were testing this, I would be using different test equipment/methods to look for a voltage drop and or high impedance, probably without needing to add any test loads.

We seem to be limited to a single volt meter and no clear picture of what is connected where so a test load, a couple of heaters, seemed accessible and definitive!
It is also no more dangerous, in unqualified hands, than attaching the inverter in the first place.

Yes. The HomeWizard P1 is pretty slow (1 second intervals) but the ET112 isn’t that much faster. You need a real fast response rate. Like 100ms.

Also. The P1 meter will soon be allowed for a battery setup (your minister of energy said so) but I would not use one.

Has been ordered.

The et340 or the Vm-3p75ct

Or do you have a single phase “fluvius” grid meter ?

The ET112 is useless all together OP has a 3f grid so he needs a 3f meter

Even for mesuring his pv installation the ET112 cant be used maybe for his ev charger?

I ordered the Vm-3p75ct as we have a 3 phase system here.

Gent is sadly a bit far away for me to just visit and diagnose it for free

To clarify i studied for electrician i have my diploma but i never worked as an electrician professionally (i will deny that i touched it)

I have wired my mp2 up myself and did its whole setup to

And i see it as a hobby so if my expenses are paid (time driving and diesel) my 3-6 hrs of talking about random stuff are free

These sunny AND windy days, the grid voltage and frequency will fluctuate gigantically (relatively speaking) because of the low-inertia electricity generation (pv-fields and wind turbines with electronic power converters). Las week I was in a factory with it’s own multi megawatt power station, ant even there the last remaining fluorescent tubes were pulsating with all the harmonics on the grid at that time.
It is certainly possible that your oscillating installation is affected by the harmonics. The impedance of the supply in the street also has an influence, coupled with the slow updating grid meter, you’ve got yourself a recipe for oscillations.

Like @Dyslexicbloke said; It can be your inverter at fault, or it is trying to do it’s job but the circumstances are making that job impossible.

I’m afraid a simple multimeter is not enough to tackle your issue. You need someone with a scope and knowledge of harmonics.

I might visit him
i have a digital scope but conecting it to the grid is just stupid so do i add a transformer 230v >12v or would this not work

Also what other mesurments would you like to make ?

If i visit im going to report what i find here for future reference

I also have a noisy mp2 so i might find out of my fan is faulty ( my fan runs frequent and noisy)

Our minister of energy said our digital meters would support net metering but guess what “Vreg” said not possible smart meters can’t do that phisics don’t allow it in Belgium apparently

So Minister of Energy is just useless

What did they do?
Sell nuclear plants to France (we now paid back the money to rent them for a few years)
Promised net metering (they where (convicted ? ) because they where not allowed to make that Decision)

Push for ev but only talk about raising power prices

Long story short, Fluvius did an investigation at the adres, determined it was their fault, they will implement a solution.