I am probably a bit late to the party on this, and maybe this is the wrong thread but I have noticed an odd behaviour with my ESS system after updating to V3.67:
The system has been in use for nearly 10 years on the same Quattro inverter, at the end of December the old CCGX was replaced with a new Ekrano unit as well as a new and much larger battery (3x16kWh Soluna units).
So the summary of the installation is:
Single phase 230v in the UK
Quattro 8000 firmware V497
MPPT150/40 with 2,2kw of solar PV
8.6kW of PV on old SMA inverters on input of Quattro metered via a Gavazzi EM24 meter on Phase 2
Ekrano GX running standard firmware (not large, not using node red)
3x16kWh Soluna batteries
With the firmware that was in the Ekrano as supplied (3.55) everything commissioned fine, at some point I upgraded to 3.67 and everything still seemed to work as expected.
Today I was taking a look at the dynamic ESS option (using the VRM implementation) and noticed that even though the battery was at nearly 100% SOC only about half of the load was being met from the battery:
The load here is a constant resistive heating load, and whilst there were small changes to the inverter output the majority of the energy was coming from the grid for many minutes. With an increase in load the inverter output increased but was still short of the load.
I looked through all the ESS settings but nothing had changed that was obvious (although the new firmware menu options are different so I may have missed something) The battery BMS was advertising a maximum discharge current of 660A so there was no limit from the BMS.
I admit to being utterly baffled and spent a lot of time looking on the forum for other users who may have had this, but similar issues normally related to current or power limits (and sometimes Dynamic ESS settings) but I was using “normal” ESS.
Getting desperate I rebooted with firmware V3.55 (the version in the Ekrano memory so no need to download) and as soon as the system rebooted it worked normally again, fully meeting the loads from the battery:
I have no idea why this fixed it, is it a bug in 3.67 with my system or was a reboot needed and the version of the ESS is not critical. For now I am happy with V3.55 and the system is working as intended but am curious if there is any input as to why this was happening.
If you need any more information let me know and I will try and help