We are facing an issue with our Victron ESS setup, where the inverter remains in sustain mode, and we are getting a low battery voltage alarm, even though the battery voltage appears to be normal.
Low Battery Voltage Alarm
The system shows a low battery voltage warning despite the actual voltage being within an acceptable range.
The battery readings seem fine, yet the alarm persists.
Inverter Stuck in Sustain Mode
The MultiPlus II remains in “Sustain” mode, instead of supplying loads properly.
We suspect this might be linked to DVCC settings or an issue with the Pylontech BMS communication. And due to sustain mode the batteries aren’t discharging at all. I have attached screenshots of the dashboard and key system settings to help diagnose the issue.
Has anyone else experienced similar problems with Pylontech US5000 batteries in an ESS setup? Any suggestions on what could be causing these alarms and why the inverter is staying in sustain mode?
Looking forward to any guidance to help resolve this!
Will that help in discharging? As of now it’s showing external control and not in sustain. Also if the battery temp. is 8 degree can this be the reason for not discharging? As Pylontech limits it with temp.
The charger settings are quite high for Pylontec, which was why I i asked. It is way out of pylons specified range. Usually that is set to 51 and 52v in the charger tab.
Do you have optimised with or without battery life on as well?