Incorrect Grid sum value on dashboard, but correct on Remote Console
The AC-Input of L1 is “way off”.
  • The Solaredge is reporting 2169 Watts
  • The Inverter on L1 is measuring 1368 Watts.
And that is about the difference of -785, as my thought outlines.
So, what I see, that your system also says “0” Consumption on L1. A wonderful 0 is very suspicious, that indicates that a “negative” consumption is calculated, and therefore displayed as 0.
From the Data - and the assumed connection paths - The system should conclude: 2169 Solar, 1368 into the multi and 6W to grid, the consumption musst be (2169-1368-6) = 795 - which again is the value we are missing on the AC In side.
Data shows, it is connected to ac-out of L1. But eventually it is configured to report it’s feedin on AC-IN? Then, the maths for consumption would conclude -1368 consumption and just display that as “0”.
And for the grid, what happens then is:
  • Sum of phases by the multi is 1370+1455-6 = 2819
  • But there is 2169 Solar reported on AC In, so total Grid-Value is 2819-2169 = 650
Can you check, that your solar inverter is configured to be connected to AC-OUT?
Settings → PV Inverters → Inverters - make sure that is set to AC-OUT.
If that IS Set to AC-Out: Change it to AC-In, save, wait a couple of seconds, then change it back to AC-Out to make sure the setting propagates again through all involved services and stuff.
Then, refresh VRM (F5) and see, if stuff is fixed. (Depending on the logging interval, it may take some minutes until vrm displayes a change)