How to Wire Orion XS to use D+ Engine Running Signal with Manual Disable Switch

The documentation for the Orion XS is leaving me unclear on the procedure to achieve the following:

  • Use D+ 12v signal from vehicle to indicate the engine is running
  • Have a hardware switch to disable the charger

Summary: both the D+ signal and a closed switch needed for charging.

The section on using the remote on/off:

https://www.victronenergy.com/media/pg/Orion_XS_12-12-50A_DC-DC_battery_charger/en/installation.html#UUID-bda15f87-aff9-bbe3-0214-5a660bbbfc84

The section on disabling Engine shutdown detection and using a D+ signal:

https://www.victronenergy.com/media/pg/Orion_XS_12-12-50A_DC-DC_battery_charger/en/installation.html#UUID-159ef088-a610-4cd9-0f6d-bd5063a6de70

Applying >8V to the L-pin overrides the engine shutdown detection and activates the charger. This can be done, for example, with an ignition switch, CAN-bus engine running detector, etc.

To force enable/disable charging (i. e. turn the Orion XS on/off) without interference from the engine shutdown detection, a remote option as given in section Connection setup for remote on/off must be wired, and the engine shutdown detection must be switched off in VictronConnect, see figure below.

I tried wiring a switch between L & H, and connecting D+ to H; this did not work.

I feel like I’m missing something simple, please help!

A.

I have now tried wiring a jumper between L & H, and a switch between D+ and H. This did not work, either. (With engine shutdown detection disabled.) As in this diagram: