How to solve an overload error on victron multiplus ii 48/3000va/35amps

how to solve an overload error on victron multiplus ii 48/3000va/35amps

A little more information about the system would be very helpful … so that we know what you have connected

First try to disconnect the output (physically). The light named ‘overload’ has 2 purposes.

  1. Overload - in this case disconnecting all load from multiplus should make the light go out
  2. Unknown error - in this situation the overload light will be turned on even in case there is no load on the unit, unfortunately troubleshooting of this case is extremely difficult, because the unit will not tell you what is problem, if you are connected via VEbus to other Victron devices the error might be on different device than the device showing ‘overload’ light - I had this situation and resulted in return of all the units as it was acting ‘strange’ and local dealer of Victron was not able to troubleshoot and Victron Europe had significantly helped, but can not help more remotely.