I got a Remote installation where they have a Problem with the VE.Bus System charge Voltage Setpoint.
System overview:
1x 10kWh Sodium Ion Battery (Natbatt)
3x Multiplus II 48/3000/35-32 3Ph/400V Configuration
1x Cerbo GX
1x Energy Meter Carlo Gavazzi over RS485
1X Fronius Symo 7.0
1x Solar Manager (Customers Choice)
This was an Old Salidomo System, where batteries got Replaced and also the Venus GX Replaced to an CerboGX. The Salidomo Batteries got Faulty after only a few years.
The Actual Problem is, that the Batteries would like to have 63.00V as Charge Voltage to use the full capacity. Also Shown in the Battery Tab on the cerbo als CVL.
Somehow the Ve.Bus System Charge Voltage will not go over 57.70VDC effective System Voltage at Charge end is about 57.3V wich make sense, because we got DC and AC coupled PV wich both can feed back to the grid.
The Settings in the Assistant and the Multis themselve are:
Absorption voltage 63.00V
Float voltage 62.00V
Charge current 35A
Is there any option to trace where the Setpoint is Comming from?
I Tried to reproduce the problem in My shop (with only one but similar unit) in here everything works fine. Also when i directly load the VE.Configre file from the Installation into my Unit.
As i can not Reproduce the behaviour in My shop, i assume its comming over Modbus from Solar Manager.
Has Anyone a idea about it?
Or is it possible that maybe some Older MPII units (Manufactered in 13/ 2021) only allow 57.70V Charge voltage “PMP482305010” (actual models are going up to 64.00VDC)
This is an override, it should not be set here unless there is an issue, if it is set, remove it and let the BMS send the CVL.
If there is no BMS or the BMS sends a lower voltage then the DVCC voltage parameter will not work, nor can it raise it above the BMS CVL, it can only reduce it.
A little Update from My side:
Today I got the Opportunity in coordination with the customer to Remotely turn off/ disconnect the Solar-Manager, to check if the problem is comming from that side (wich should not be, becasue the battery-system is self regulating)
Summary was, that the CVL changed a short period for some minutes to 57.4V and then get back to its known 57.7V so there is no real effect in it. Except the short glitch to 57.4V wich makes me a bit curious about.