I have a 3xMP-II 5kVA installation.
When I set the grid setpoint to 11.000W it only reaches 6700W and charges the battery with 88 A
Hardware is not limited:
Possible charge current: 3X70A = 210 A
DVCC: Max charge current battery: 590A
I have a 3xMP-II 5kVA installation.
When I set the grid setpoint to 11.000W it only reaches 6700W and charges the battery with 88 A
Hardware is not limited:
Possible charge current: 3X70A = 210 A
DVCC: Max charge current battery: 590A
What type of battery? Does the battery perhaps have a BMS that reports a lower CCL to the Victron system?
It’s 6x Pylontech US5000 battery, connected over 3 cablesets (could have 375A).
The DC charge current is not limited in DVCC.
The AC max grid current is set to 32A.
Charge Current Limit is now 600A so battery is feeling good.