Help Understanding Split-Phase vs Parallel Configuration – Two MultiPlus Inverters, One AC Line
Hi everyone,
I’m looking for some clarity on our Victron setup and whether it was installed correctly. We live in Guatemala and have two Victron MultiPlus 12/2000/80 inverters with one battery bank. Our home has a single AC line (120V) — no split-phase wiring, no 240V appliances, and no second AC load.
The system was supposedly originally configured as split-phase, but we believe that’s incorrect for our house. Our understanding is:
  • Split-phase configuration assumes two active AC lines (L1 and L2) in the house to distribute loads across both inverters.
  • Since we only have one AC line, it seems that only one inverter is properly powering the house, and we’re not getting the full capacity of our system (batteries and inverter power).
  • The solar company now wants to charge us to reconfigure to parallel single-phase, even though that seems like the correct setup from the start for a single-line home.
  • Or, they are telling us we need to hire an electrician to rewire our house for two AC lines.
Questions:
  1. Is it possible that both inverters are technically “on” in split-phase, but only one is actually doing meaningful work if the house has just one AC line?
  2. Could this explain why our battery drops too low or the system shuts off under moderate loads at night?
  3. What’s the correct way to set up a two-inverter system with a single-phase house and one AC output line?
  4. Could they have wired it as split-phase and simply left one inverter’s output unconnected?
  5. Is there any situation where split-phase is okay with one AC line?
A little backstory: The system worked great for a few years any time of day, then the second inverter had a failure and it was sent in to be replaced. When they took that second inverter they rewired our system to work with one inverter and the voltage couldn’t keep up with the power demand at night. ONLY after the second inverter failed and was taken. So is it even possible that it was originally split-phase abd working, and suddenly now it is not (after having the new inverter reinstalled).
We’d love any feedback, diagrams, or advice. We are considering buying an MK3-USB ourselves to reconfigure it if needed. Thanks in advance!
  1. You need to determine what is connected to the AC-Input of both inverters.
  2. To be determined
  3. The correct way is to configure both inverters for parallel operation, with the input lines combined, and the output lines combined.
  4. You need to determine how it is wired, but that is possible.
  5. It is possible to configure the inverters so split-phase is produced from a single phase 120v input by having the second inverter generate the L2 by drawing from the battery (disabling “Switch as Group” in VEConfigure).
If you have 120V service, with a utility meter for 120V service, and a breaker panel with only one line input, they should not have set you up for split phase. Is it possible the breaker panel looks like a split-phase panel so they assumed?
As you have no 240V appliances, you have no need for split-phase (unless you want to upgrade later).