Hey Sven,
DVCC:
Hey Nordbaum3936, see earlier post where I place screenshots from my DVCC settings.
You could try turning off Limit charge current and see whether it starts feeding power back when you’d expect it to.
Hey Sven,
I hope I can test that tomorrow as it’s going to be sunny and than the battery should get charged 100%.
Hey Sven,
Before switching it off, I had this situation when reaching 100%
And when it was fully loaded, you can see that it throttles:
I then switched off the Limit Charge Current and now it seems to be injecting any excess solar energy:
So that does seem to do the trick somehow, but do you happen to have an explanation as to why? Want to try and understand why this specific toggle makes the difference, as the limit was up to 240A prior to switching it off.
That could also be a setting in DESS. You could temporarily disable DESS and just use ESS to see whether it keeps feeding power back.
What are your charge and discharge power settings under DESS for the battery?
This should be set to 5 kW or 5.5 kW on your system.
As for disabling DVCC limit charge current, it may work because then you no longer have two captains on one ship. The BMS says, “I want 0 A for now,” while the DVCC limit says, “I want a maximum of 240 A.” The MPPT RS then drops anchor.
It could also be happening now because your DVCC charge battery limit is set to 56.3. You could increase it to 56.8, assuming you have a Voltsmile V10. Check the manual for your battery type.
I do indeed have a Voltsmile V10, and that value is currently set to the default of 56.3. I’ll try that again afterwards as well.
You could also check in VRM > Advanced: click Widgets at the top right, then “Gateway”, then turn on System - Battery Voltage And Current. Then you can look back to see whether it did indeed hit 56.3 V this afternoon, at the moment it stopped feeding power back.
With the settings at 56.6V and DESS switched off, I get the feeling that the system keeps throttling. The PV Charger normally delivers 3 to 5 times the power of the PV Inverter (depending a little on the time of day):
Trying to understand why the system does this and whether it can be ‘controlled’ using some kind of parameter.
So, was DVCC limit charge current turned off and charge battery set to 56.6 V?
Ah, the limit charge current was no longer switched off. I’ll test it again tomorrow.
You can even go higher, you know. The Voltsmile V10 manual gives 56.8–57.6 V as the maximum. You could safely set it to 56.8 V. Otherwise, DVCC will probably put the brakes on too early, which will stop feeding electricity back into the grid again. Unless, of course, the manual that came with yours says otherwise.
Hi Sven,
Had to wait for better weather, but I’ve just reached 100% again. And even though I have the battery set to 56.8V, DESS switched off and the charging current switched off, it still keeps ‘adjusting’ the input from the PV Charger so that my Grid consumption is virtually nil:
It’s not a major problem, but I’m just trying to understand why it no longer wants to feed anything back into the grid.
Did another little test.
Initial situation:
Air conditioning switched on (AC load increases, and the PV charger also increases while the PV Inverter stays the same):
Air conditioning switched back off:
All of this happened within a few minutes while the sun was shining brightly.
And afterwards, I switched on the heat pump as well:
Is there anything else I could check?