GRID Feed-in with DESS and battery at 100%

Hi,

I’m a newbie and have the system now active for 1 week and really like its capabilities.

This is my current setup:

What I noticed is, that when my battery is at 100%, the system stops taking energy from the PV charger and doesn’t feed it back to the grid anymore.

Even though I have these settings active:

I have a dynamic contract and would want the system to inject any excess energy into the grid, especially on sunny days when the batteries can easily get charged.

Any suggestions/experiences?

Thanks in advance!

And what are the ESS settings in VRM for selling back to the grid?

This screen here

Hey Peter,

It’s in Trade mode:

Yes, then it should be able to feed power back :wink:
And what does your plan for the whole day look like?
Those are the three graphs on VRM.

Yeah, that’s what I also thought, but have now experienced it twice that when the batteries are at 100% and even though there’s still plenty of sun out there (and my PV inverter is still injecting energy into the grid too), the PV charger basically shuts down all 4 strings :roll_eyes:

These are my graphs for today:

The graph shows that power is indeed being fed back during the day (the orange “solar to grid” blocks, and quite a lot too). And your very first image at the start of your topic also shows 4 kW being fed back. Do you have a point in time when, according to you, no power is being fed back?

Not yet, have forgotten to take screenshots when it was the case. The moment I have that situation again, I’ll take screenshots and post them here.

Looks like one inverter on a three phase grid connection.
In some country’s the netcode is limited to inverting max 5000W± on one phase in 1 three phase grid connection to keep the grid stable. My guess is that the solar panels al throttiling back beause of this limit. In you first screenshot I see you inverting 21.3A back to the grid what is around the max that is allowed. Should be around 21.7±A

Hey Sven, it’s a three phase grid connection, but I can inject op to 32A here. Screenshot from my cell phone this morning:

Batteries are loading now. If and when they reach 100% (depends on the weather of course), I’ll post an update.

Hi,

Batteries where almost full and you can see that my 4 strings are producing sufficient energy on the PV Charger:

A few moments later with same solar energy (you can see that on the PV inverter), it really throttles the strings down and tries to stay around 0 GRID:

When this happens, also look at the sell-prices.
If Sell-Prices are negative, DESS will restrict Feedin as well.
(I doubt that was the case at 17:00, but don’t know your exact contract)

What inverter type do you use?

Prices were not negative yesterday at 17:OOHr:

Inverter is SMA Sunny Boy 4.0, 10 panels, south-east oriented.

I was meaning your victron intverter. Miltiplus XXX? MultiRS?

I’m thinking a MultiPlus, because it can handle ESS settings via the Cerbo in conjunction with a SmartSolar MPPT RS.

Hi Kris, why are the MultiPlus and the SMA Sunny Boy connected to the same phase? This is the reason why it can exceed ~21.5A—both inverters are running on the same phase.

If you intend to feed a significant amount of power back into the grid, it might be better to move the Sunny Boy to a different phase.

Ooops, misunderstood: have a MultiPlus-II GX

Prior to the MPPT from Victron the solar panels were managed by a SolarEdge inverter. Both the SolarEdge & SMA were also together on L1 and they have always been able to feed back more than 21A together. You can see in one of my screenshots that I’m injecting 26.8 A and we’re allowed to go up to 32A & 10K injection.

Hi Kris, I’ll switch to Dutch for a moment, as that makes it a bit easier to explain.

You’re right that it’s possible, but there are strict rules for this in Belgium. With the way it’s currently connected, you’re violating the grid code. You’re only allowed to feed a maximum of 5,000 watts into the grid on a single phase.

The reason you’re feeding in more is that both the Victron inverter and the SMA inverter comply with this rule. The Victron inverter can see how much power is actually being fed into the grid, and the SMA Sunny Boy on one phase is safely below 5,000 watts. So if the battery isn’t full yet, the Victron inverter will neatly charge it with all the power it can, to stay below the 5,000-watt limit. However, it has no control over the SMA inverter.

To comply with the rules, the Victron inverter will therefore occasionally curtail the solar panels to keep the output around 5,000 watts.

But the solution I suggested—moving the SMA inverter to another phase—isn’t allowed in Belgium either. See point 3, as well as the other rules that I think your installation is currently violating. Perhaps you have an exemption from the distribution system operator?

When combining solar panels and a home battery on a single phase in Belgium, very specific rules apply under the Synergrid C10/11 requirements. The exact rules depend entirely on the type of inverter you choose (hybrid or AC-coupled).

Here’s a summary of the rules:

1. Power limits for each type of installation

  • Scenario A: One hybrid inverter (DC-coupled)
    With a hybrid inverter, both the solar panels and the home battery are connected to the same unit. The inverter manages the flow of energy to your home, the battery and the grid.
    • The rule: The nominal AC output of the hybrid inverter must be no more than 5 kVA. It doesn’t matter how many kW of solar panels (DC) you install on the roof; the output to the grid is the limiting factor.
  • Scenario B: Two separate inverters (AC-coupled)
    Do you already have an inverter for your solar panels and want to add a home battery with its own separate battery inverter? In that case, they’re treated separately.
    • The rule: The solar inverter can be no more than 5 kVA, and the battery inverter can also be up to 5 kVA separately. So a separate battery inverter doesn’t eat into the capacity of your solar panels.

2. Simultaneous injection is prohibited (EnFluRi sensor or P1 port)

Although an AC-coupled system can have two 5 kVA inverters (10 kVA in total), you must never inject more than 5 kVA into the distribution grid at the same time.

  • To ensure this, you must install an EnFluRi sensor (Energy Fluctuations Regulating Installation) or use a smart connection via the P1 port on your digital meter.
  • This sensor ensures that if the solar panels and the battery try to feed power into the grid at the same time, the total output at the point of connection is strictly limited to 5 kVA.

3. Physical requirement: Everything must be on the same phase

If you have a three-phase connection at home but install a single-phase battery and single-phase solar panels, Synergrid has a strict requirement: they must be connected to exactly the same phase. So you can’t spread them across different phases to supposedly balance the grid.

4. The rating plate is binding (no software-based limiting)

Network operators such as Fluvius look solely at the nominal power shown on the inverter’s rating plate. If you buy an 8 kVA inverter and limit it to 5 kVA in software, the Belgian grid code does not accept this for a single-phase installation. The physical unit must not exceed 5 kVA.

5. New grid requirements: Automatic voltage regulation (Q(U))

Following recent updates to the grid code, all approved inverters on the Synergrid C10/26 homologation list must be equipped with Automatic Voltage Control via Q(U). This means that your inverter will automatically and temporarily curtail its output or shut down if the voltage on your particular phase in the street gets too high.

Hey Sven,

Thanks for the explanation! It does seem strange, though, that none of the inspection bodies here has ever said anything about this during any of the inspections I’ve had done.

During the renovations a few years ago, we switched from single-phase to three-phase power (geothermal heat pump, EV, induction hob, …).

After that, I had that SMA inverter added (which meant I could go up to 9kWP: 5 from the SolarEdge and 4 from the SMA). It passed inspection without any problems.

Then I had a charging station installed: passed inspection without any problems.

Last week, I had the Victron system installed: passed inspection without any problems.

Each time, the installation was inspected by a different official body.

If I understand correctly, then, my installation doesn’t comply with the regulations? It’s pretty astonishing that no official installer or inspection body has ever brought this to my attention :see_no_evil_monkey::see_no_evil_monkey:.

I can also understand the point about limiting it to 5000W, but that is definitely not what’s happening in the situations I’ve described here:

Once the battery is full, I would expect it to feed the remaining energy back into the grid, but that is absolutely NOT happening. I’m trying to understand why it’s doing that, and whether there might be a setting that’s preventing it from doing so at that point?

No, it isn’t the explanation for everything you see, indeed. On the one hand, it’s nice, of course, that it’s all passed the strict inspection in Belgium :slightly_smiling_face:

What are the settings like on DVCC?