Hi Kris, I’ll switch to Dutch for a moment, as that makes it a bit easier to explain.
You’re right that it’s possible, but there are strict rules for this in Belgium. With the way it’s currently connected, you’re violating the grid code. You’re only allowed to feed a maximum of 5,000 watts into the grid on a single phase.
The reason you’re feeding in more is that both the Victron inverter and the SMA inverter comply with this rule. The Victron inverter can see how much power is actually being fed into the grid, and the SMA Sunny Boy on one phase is safely below 5,000 watts. So if the battery isn’t full yet, the Victron inverter will neatly charge it with all the power it can, to stay below the 5,000-watt limit. However, it has no control over the SMA inverter.
To comply with the rules, the Victron inverter will therefore occasionally curtail the solar panels to keep the output around 5,000 watts.
But the solution I suggested—moving the SMA inverter to another phase—isn’t allowed in Belgium either. See point 3, as well as the other rules that I think your installation is currently violating. Perhaps you have an exemption from the distribution system operator?
When combining solar panels and a home battery on a single phase in Belgium, very specific rules apply under the Synergrid C10/11 requirements. The exact rules depend entirely on the type of inverter you choose (hybrid or AC-coupled).
Here’s a summary of the rules:
1. Power limits for each type of installation
- Scenario A: One hybrid inverter (DC-coupled)
With a hybrid inverter, both the solar panels and the home battery are connected to the same unit. The inverter manages the flow of energy to your home, the battery and the grid.
- The rule: The nominal AC output of the hybrid inverter must be no more than 5 kVA. It doesn’t matter how many kW of solar panels (DC) you install on the roof; the output to the grid is the limiting factor.
- Scenario B: Two separate inverters (AC-coupled)
Do you already have an inverter for your solar panels and want to add a home battery with its own separate battery inverter? In that case, they’re treated separately.
- The rule: The solar inverter can be no more than 5 kVA, and the battery inverter can also be up to 5 kVA separately. So a separate battery inverter doesn’t eat into the capacity of your solar panels.
2. Simultaneous injection is prohibited (EnFluRi sensor or P1 port)
Although an AC-coupled system can have two 5 kVA inverters (10 kVA in total), you must never inject more than 5 kVA into the distribution grid at the same time.
- To ensure this, you must install an EnFluRi sensor (Energy Fluctuations Regulating Installation) or use a smart connection via the P1 port on your digital meter.
- This sensor ensures that if the solar panels and the battery try to feed power into the grid at the same time, the total output at the point of connection is strictly limited to 5 kVA.
3. Physical requirement: Everything must be on the same phase
If you have a three-phase connection at home but install a single-phase battery and single-phase solar panels, Synergrid has a strict requirement: they must be connected to exactly the same phase. So you can’t spread them across different phases to supposedly balance the grid.
4. The rating plate is binding (no software-based limiting)
Network operators such as Fluvius look solely at the nominal power shown on the inverter’s rating plate. If you buy an 8 kVA inverter and limit it to 5 kVA in software, the Belgian grid code does not accept this for a single-phase installation. The physical unit must not exceed 5 kVA.
5. New grid requirements: Automatic voltage regulation (Q(U))
Following recent updates to the grid code, all approved inverters on the Synergrid C10/26 homologation list must be equipped with Automatic Voltage Control via Q(U). This means that your inverter will automatically and temporarily curtail its output or shut down if the voltage on your particular phase in the street gets too high.