Hello,

Im using a Ess Multiplus 5kva with a Pylontech setup.
Can anybody tell me how I can use the output1 for mij house.
And the output2 for a salon?

I want the house Powered from the battery’s and the salon needs the Energy from the grid.

The idea is that I dont want to come home after work and that my battery is empty because my salon is taken everything :sweat_smile:

Has anybody an idea how to do that.

I already got myself a et112 for messuring but it didnt do the job I wanted, connected on the output as a ac load didnt work also tryed to use it as a grid meter.

Greats,
Alwin Tichelaar.

Move the Salon circuit upstream of the multiplus if it needs to be only powered 24/7 from the grid. The ACOUTs are parallel connected with ACOUT2 disconnecting (relay) when there is a grid failure. The system cannot discriminate between the two and why you don’t see two instances of ACOUT in VRM or the GX.

Thanks for your answer, then im gonna move the salon to the grid connection.
Thought this was possible :sweat_smile: