What i have to do to forcefully discharge battery to grid.
it tried with ESS Mode 3 (external Control from NodeRed Description)
and Setpoint to 20000 or -20000.
For the MultiRS you use the Multi RS (control) nodes.
Setting ESS mode to 3 allows you to control the ESS power setpoint manually from NodeRed
it may be needed to keep sending the requested ESS power setpoint every xx seconds.
In a 3 phase system with 3 MultiRS’s you can (and need to) control each MultiRS ESS power setpoint individually
If you have a Canbus connected VM3P75CT Grid meter (and it is properly configured in the MultiRS settings) your requested value will be referring to grid draw or feedin as measured by the VM3P75CT
Without this grid meter your requested ESS setpoint refers to the AC-in of each of your MultiRS’s
This is what I was able to figure out so far, and it works quite well for me. I had the system running under NodeRed control for about a month but now allow DESS to manage my system automatically most of the time.