Hello there
Since i have spent a lot of time on research and could not get a answer i am hoping for some clarification here.
I have a setup with 6 multiplus5000/48 and 28kwh storage on Pylontech Batteries. 2 450/200 MPPTs attached to 7 PV Strings.
The multis are configured as ESS and everything works as expected and is great so far.
But there is one thing i do not understand:
In case of a longer Power outtage i want to use a Generator to charge the batteries in case the PV power is not sufficient. I am Talking about serious generators, one is a 20 kVA (Yanmar engine with a MeccAlte Generator) the other i tried is even bigger, 100 kVA (GCB engine with Leroy Somer generator) so high quality stuff with lots of power.
The problem i am facing is, if the Multis (or Quattros, tested both) are configured as ESS they do weird stuff when charging the batteries; the 20 kVA starts to oscilate with Voltage and Frequency and the Circuit breaker is triped within a few Seconds) the 100kVA also oscilates with Voltage and less Frequency but the Current goes up like hell and the Controller of the Generator opens the GCB and shows a Error message (sometimes voltage, sometimes frequency).
Thinking outside the box, both gensets can do grid parallel i was thinking “hey lets give it a try and connect the genset to AC out” (again, the gensets can do grid parallel meaning they synchronise their voltage and frequency with the inverter, close the circuit breaker and gently start to push energy)
without ESS this works fine, even if i don’t think the inverters are made for this setup (but if they can handle a PV on AC out, they can also handle a genset don’t they?) the genset synchronises and starts to push power in the system, the power goes backwards in the batteries (just make sure the BaseLoad of the genset is less than what the batteries and inverters can handle ;-))
but if i enable ESS i have exactly the same behavior. They can start to generate huge reactive power. The frequency of the genset starts to oscilate (genset shakes) until the controller disconnects immediately because it detects a “unstable grid”.
So why is the charger behaving differently if it is setup as ESS than other? And what does it do exactly?
what would be the right setup if i want to charge my batteries with a Genset during a power outtage? Is there any other solution to feedback to grid the exess PV power without ESS configured?
Btw. the issue is only there if there is no grid, if i connect the Genset no matter to AC out or AC in, and do a Grid parallel application everything works (but there is no reason to let a genset running when grid is available )
thanks in advance for your reply and help