I have a 3 phase Multi RS Solar A443 system, running stable on firmware 1.26. When i upgrade to firmware 1.27 one of the units throws Error #59 ACIN1 relay test fault while the other two operate without issues. When i downgrade to 1.26 the “faulty” unit operates normal again. Did something change in the ACIN1 relay tests in firmware 1.27? Is this a hardware malfunction or a firmware bug?
Hi @rhernaus
Engineers are looking into it now. Appears to just be a false alarm associated with this update.
But will confirm more
A quick fix has been released in an update v1.28
Wow amazing. I have installed v1.28 and can confirm the unit now operates without issues.
I had exactly the same problem with firmware 1.27. Since installing it, I always had the relay error. After updating to version 1.28, the error disappeared.
Thank you Guy