This morning I updated my Multi-RS units (A443 units) to firmware 1.29. One unit is now stuck in this error “#59 ACIN1 relay test fault”.
It looks like this issue: Error #59 ACIN1 relay test fault on firmware 1.27 , but I encounter it on 1.29.
It has been working without any issues on 1.26 - 1.28 versions.
I have a 3-phase setup, and now the entire setup disconnects, because of 1 unit with this issue.
Anything changed in this area that can explain this?
Not sure what you mean though, but when I start up the unit, it does the usual rattling, pops up with the mesage that acin relay is open, then somewhat later the error message pops up. That message stays there.
Does the unit connect’s to the grid and uses it after the ‘rattling self test’?
What i am trying to establish is if the messge is spurious or there is a hardware problem.
If it is hardware then the unit goes for a warranty assesment if it is a message displayed that does not need to be there then more investigation needs to be done.
I do not think it really connects. It shows the AC-In voltage etc. It does the self test, and then reports the error. I do not see it actually close the connection to the grid.
I think you are pretty much at the point of an RMA as there is not much more that can be done. The other reason being you were already having some issues before this. Not big ones but still creates the suspicion.
I created from the advanced page a screenshot from the internal relay state. Is this the relay we are talking about? And if so, isn’t it actually closing for some time? Not sure what I am actually looking at.
No, really… they are four (4) independent ones…
Two in series on the live and two on series on the neutral, just like on the schematic.
And as the relay board is an independent one, it can be taken out and examined/tested.
I would do that for my system, but I am not encouraging anyone to do the same…