Easysolar II GX - get correct SOC with internal battery monitor

Good morning,

I am having trouble with proper SOC readings in a new installation with an Easysolar II GX in combination with lead acid batteries and no external battery monitor or shunt.
It is our first installation with an Easysolar (all other are Multi or Quattro with external MPPT and Cerbo GX) and the only installation using victron components with lead acid batteries (all other are either not Victron or use lithium batteries with external BMS). So this is somewhat new to me. I tried to look into similar threads, but didn’t find a solution yet.
The problem is, that during normal operation (MPPT charging the batteries during the day hours), the SOC never goes to a 100%. I am not really sure, if that is, because the batteries really don’t get filled properly, or because some settings for the internal battery monitor need twisting. The only time I saw a 100% charge was after a low battery condition that triggered a grid connection and therefore a full charge (set via virtual switch in the multi).
I tried a few things, (including having higher charging voltages set in the MPPT than in the multi), but am kind of out of ideas now, and when I check the data in VRM some questions come up.
Here are my current settings:
MPPT - Battery Tab

Multi - Charger Tab

Multi - General Tab

VRM - SOC

VRM - Battery Voltage and Current

VRM - MPPT State

When I look at the voltages in VRM, I see a maximum charging voltage of 56.1V during absorption phase. That is confusing, because it does not correspond to the settings in the MPPT (which is set to 57.6V with a temp. coefficent of -120mV/°C and a battery temp. of around 31°C → should give around 56.88V).
On the other hand, it kind of fits with the charger setting in the multi (set to 56.8V with same coefficent → should give around 56.08V).
Could it be, that the multi setting is overwriting the MPPT setting, or is this just a coincidence?
The source of charge for the battery is clearly solar (because of the VS setting, grid is usually disconnected). So I don’t understand, why the battery is not further charged, if it is not full (clearly there is excess solar energy, while the MPTT already changed to float).

What am I missing?
Any help or pointers in the right direction are appreciated.
Tim

Hi, this is expected, the internal metering is not accurate and has to estimate what the mppt is producing. The only solution for accuracy is to configure an external shunt/bmv.

Hi, thanks for the quick reply :slight_smile:

Is that confirmed by experience?
I am asking, because the CCGX manual suggest something different, see 8. Configuration
To quote the relevant sentence directly:

No battery monitor is required as long as all MPPT solar chargers are Victron products and are connected to the CCGX. The CCGX will continuously read the actual charge current from all solar chargers and send the total to the Multi (or Quattro), which then uses that information in its SoC calculations.

That aside, the question about the “wrong” charge voltages as described above remains unclear to me. This should not be related to an external battery monitor, or not?

Try to Configure the same charging voltages in the MultiPlus and the MPPT.

A SmartShunt/BMV is way more accurate than the internal battery monitor of the MultiPlus.

Thanks for your input.
That is the first thing I had done, before I even realized, that something is not right.
The SOC always got stuck at 85%, which seems to be the expected behavior described in the above linked manual (section 8.2.5) :

While the Inverter/Charger is in bulk, the SoC will not rise above the value as set in VEConfigure for the ‘State of charge when Bulk finished’ parameter on the General tab; default 85%. In a system with solar chargers, make sure that the absorption voltage as configured in the MPPT is slightly above the same setting in the inverter/charger. The latter needs to recognise that the battery voltage has reached the absorption level. If it doesn’t, the SoC will be stuck at the earlier mentioned End-of-bulk percentage, default 85%.

Edit:
does somebody know where to find the mentioned status in the new UI:?

In the System status menu, verify that the option ‘Use solar charger current to improve VE.Bus SOC’ is set to On. Note that this is not a setting - it just an indicator of an automatic process.

It could also mean your battery is not reaching the full time in absorption or it’s on adaptive. Maybe set that to a fixed time and make it not short.
So technically undercharged?

Further question, is this a bank made up of 12 batteries? If so do you have balancers?

Can happen if ess is programmed - or Dvcc svs.

Have you checked with a meter. Voltage drop over a cable can be mean as well.

Settings -system set up - system status

How would I find out, if they are undercharged?
Do you mean the settings of the MPPT that are “hidden” behind the “expert mode” switch?

Its 8 batteries, no balancers. They have been tested and tried in this configuration for some time, so I don’t think the batteries or the wiring are any problem tbh.

No ESS.

How would the Multi charger settings be written to the MPPT by activating DVCC? As far as I understand, SVS only defines a commen voltage sensor?!

I have not confirmed with a meter yet, have to get on site for that again.

Well, thats also what the manual says, thanks. I was specifically referring to the new UI because I don’t see “System Status” anywhere…

Knowing this then you need a much longer absorption time.

My screen shot is the new UI. Hit the gear at the bottom right of the screen

my settings - system setup page looks like this:

no system status and no gear either… (even after scrolling down)

Why does the number of batteries influence the absorption time?
So I should switch to expert mode in the MPPT and put a custom absorption time (like 3h maybe?)? How do I prevent overcharging?
Again, does any of this explain, why the voltages are “off”? I find that part most confusing…
Thanks for your help by the way :slight_smile:

Voltage (verify with a meter at the battery Terminals) and mostly keeping an eye on battery Temperature.
Other checks would need to be each battery voltage and also possible keep a maintenance thing where the batteries are rotated. Ohms law is a hard task master)
Are they FLAs?
To know more refer to energy unlimited
And wiring unlimted.

Weird. It is at the bottom…

no, maintenance free. nobody there to regularly check water levels and refill.
8x C&D Technologies AES 12-2170F if I remember correctly.

indeed, that is weird. DC loads are the last visible line for me…

They are on by default anyway.
And not user changeable

Wondering maybe because I have some mods and super user access on it is visible to me.

hm, ok. the manual just said to check, and then I couldn’t find it. So I think it should be visible normally. Checked on two different installs with Cerbo GX, and it is also not there. The GX in the Easysolar is brand new, and on recent firmware. So don’t know, why not showing…
Edit: you are right, Venus manual says

This menu is read-only and cannot be used to configure settings. It is only visible for Access level Superuser, and the visibility and state of each flag depend on the system configuration and connected devices.

Glad you found it. It was knocking around my brain but couldn’t figure out where I saw or learned it .

Changed to superuser to confirm, that the communication between mppt and multi is working in this regard. everything seems ok. went on site today and changed to 3 hours fixed absorption time. lets see, if that does the trick. I am still not sure about the voltage levels though. something seems off to me… will report back after a few cycles.

Getting back to this topic after trying for some days with fixed absorption time of 3 hours. Sadly, that didn’t do the trick. At least the SOC now rises over the 85% mark, usually up to 88, sometimes to 90%. But that is far from 100% even though there is enough solar power. I am a bit lost, what kind of setting I could still tweak, to get the desired behavior… If anybody has other idea, please share.

Also saw your temperature compensation figures.
How hot are they getting or what is ambient? I thought your mentioned around 30. What is measuring it in the system though? Is there a temp sensor?
That would also affect your charge voltage.
From your graphs it looks like it is reaching the right voltages there though.
A smart shunt or bmv is the way to go though.

The other possibility of course is that you have some unwell batteris there. Or loose connection?
Tried rotation of the batteries in the bank?

yes, around 30°C measured with a temp sensor on the batteries as per manual. So after adjusting the absorption time, the charging voltages seem to be ok (considering the temp). No further question there.

could be, but highly unlikely. they were just fine before switching to the easy. but will still check, if I am on site again.

I have seen that answer a lot now, and I start to believe, that I should just go that road.
But I must admit, that I still find it irritating/disappointing for two reasons:

  1. the selling point of an easy is to have an all in one device. And as per manual, what I am trying should easily be possible without BMV or shunt. Usually the victron manuals are quite good/reliable. Especially if something is mentioned specifically, it is usually correct.
  2. when the multi is charging the batteries, the SOC goes to a 100% with an even lower charging voltage that the MPPT (as per manual) and in about the same time (~3h). How can that be, while all the necessary calculation data is obviously there (as visible in VRM).

I had similar problems with wrong battery voltages etc (I’m using LifePO4 batteries)

I tried many different settings but nothing seemed to work for me - even after posting on this forum getting some helpful tips, but didn’t solve my problem.

The only thing that worked was to install a Victron Smart Shunt to monitor voltages and currents accurately, and this did the trick. For the last couple of years everything has worked perfectly.

It may not cure your problem, but having the Smart Shunt did for me.