Just heard back from the DNO - they’ve now granted islanding and said:
Earthing
Whilst the existing earthing arrangements can be retained, it is your responsibility to ensure that adequate earthing arrangements are made for your installation in accordance with the current IEE Wiring Regulations (BS7671).
You must ensure the earthing of your generator complies with the requirements of G99.
Anyone familiar with all of the requirements there?
I believe the important part is this? -
When a low voltage generator (such as a standby generator, solar inverter, or battery energy storage system) operates in island mode as a switched alternative to the public supply, it must not rely on the distributor’s TN earthing system.
So i’ll need a TT (earth rod) to be able to operate any (non double insulated) loads in island mode.
What i’m not 100% clear on is - can I have an earth rod installed and join that to the existing earth from the grid (TN-S) - that way I get “the best of both worlds” and have both a local earth and the reassurance of the grid earth being there should there be any issues/increases in resistance/impedance of the local earth rod - as well as not having an issue with nearby surfaces with different earth potentials.
Reading this guide, I read that as I can have the TT/earth rod connected to the existing main earth supply, which fits with what (if I understand correctly) @David2 said - and if I read it correctly, it says that you can leave the supply earth connected in island mode (it’s the line and neutral connections which must disconnect, which is handled by the Multiplus), you just can not rely on it - i.e you need a TT earth as well.
If I am correct here and the answer is yes [a TT earth electrode an be connected to the existing TN-S earthing system so you have both], is it ok for that TT earth to be connected to an outbuilding?
In my case, I have henley blocks splitting off my house consumer unit with a supply (and 80A MCB) to [16mm2] armoured cable feeding my garage which is a separate “building” at the side of the house. This is where the Multiplus II and solar inverters are and it would be very convenient to have an earth rod installed next to that and fed in to there, which would connect to the garage consumer unit (and earth fed in to there via the armoured cable).
(All end user circuits in both the house and garage are behind RCBOs).
The DNO letter also states:
Earthing Export
The star point of your generator must not be connected to our earth when operating in parallel with our Distribution System.
I believe this refers to not connecting Neutral and Earth when connected to the grid?
In which case I believe that is automatic on the Victron, per Nick’s post above (on loss of mains it opens a relay disconnecting from the grid, before joining earth and neutral - which it will reverse before connecting back to the grid).
Thanks,
Ian