I have 1 x Dyness DL5.0C and want to connect it with my Victron Energy Multiplus 2 48/3000 GX and I need some help with charger settings. I connect it via CAN 500k.Maybe someone have configs? Dyness support doesn`t give me some feedback.
in general tab
48 52 48v
charger tab
absorption 55v
float 54.5v leave rest as is
in ess assistant bms other types
sustain 52v
dynamic cut off 48 v all three
restart offset 2v
type b cable or use one marked viltron from dryness
hope this helps
Sorry just seen your other comment I found that on an install but when I do the pylontec I also drop them down a tiny bit also it avoids any over voltage alarms
Mine get to 100% on those settings
Regards Allen
Yup, i find that too.
I’ve never had a system with a large voltage drop (we don’t skimp on cable size, and keep things short) but if i did i might go up a bit.