Setting up Dynamic ESS for the first time: maximum discharge power / maximum charge power

After reading various guides and carrying out an extensive search online, I still can’t work out the correct way to calculate and enter the maximum discharge power and maximum charge power in Dynamic ESS.

My installation consists of 3 x 48/8000 MultiPlus-II units and 12 Pylontech US5000C/48V batteries (57 kWh) in a 3-phase setup.

The maximum discharge and charge current of the Pylontech batteries is 100 A.
The 48/8000 MultiPlus-II has a continuous output power of 6400 W and a maximum charge current of 110 A at 48 V.

In my opinion, the MultiPlus is the limiting factor here.

For the DESS settings, I think the correct values to enter on the second page of the Dynamic ESS setup are as follows:

Maximum discharge power: 48 V (battery voltage) x 100 A (max. discharge current) = 4800 W x 12 (number of Pylontech batteries) = 57,600 W → 57.6 kW. However, as mentioned, the MultiPlus is the limiting factor, since it can deliver a maximum of 6500 W per phase. This means the maximum discharge power should therefore be 3 x 6500 W = 19,500 W → 19.5 kW.

Maximum charge power: 48 V (battery voltage) x 100 A (max. charge current) = 4800 W x 12 (number of Pylontech batteries) = 57,600 W → 57.6 kW. However, as mentioned, the MultiPlus is the limiting factor, since it can charge at a maximum of 110 A per MultiPlus at 48 V. This means the maximum charge power should therefore be (3 x 110 = 330 A charge current) 48 V x 330 = 15,840 W → 15.84 kW.

If this isn’t correct, I’d appreciate it if someone could explain how to calculate this properly, as it’s not described anywhere else and I’ve found various other calculations that I’m not sure are correct.

Hi…tricky topic. You can’t really calculate this value. Based on everything you’ve written, I also assume the MP2 is the limiting factor, but only when it’s running at its optimum. As soon as it gets a bit warmer, its output drops too. There are also the BMS units in the batteries, which limit the output, or the voltage rises and the MP2 reduces its output. You won’t get an answer accurate to the nearest watt by calculating it.

My recommendation, or what I did: first enter the MP2’s output, or perhaps a little less, then keep an eye on whether the system generally reaches that value while charging. I also gradually worked my way towards the optimal setting. It’s a bit of a faff…I admit. However, with Victron systems in particular, there are a lot of factors that affect the maximum charge rate.
In my experience, I can tell you that it’s good if the value is roughly right, but the last watt doesn’t matter, because DESS adjusts its plan every hour. If it hasn’t reached its target, it looks for the next opportunity to make up the difference.

Just don’t make the mistake of entering the absolute maximum possible figure from the manuals; the system generally won’t reach it because another factor will get in the way.

Good luck, and give yourself a bit of patience and time to start with.

I’d just enter that 15 kW here. DESS also takes into account (eventually) all the other (much more important) limits you set on the device itself, such as the maximum current on AC IN and the maximum charging and discharging current. You can also enter the converted value of 110 A, since it can’t go any higher anyway. Overall, it won’t make any difference.

Which is what the maximum power is actually. So if you want It to if it can work that hard set it there. (Similar to the speedometer on a car can go up to 220kms/he doesn’t mean you drive it there all the time but the potential is there).
However if you didn’t want the system to charge and discharge the max possible (on paper), or there are grid or contract restrictions, then you set it lower.

So it is a bit about calculating and a bit about wants/needs.

Have I misunderstood something? This is about DESS. The maximum charging power in the configuration doesn’t actively regulate anything; it’s used solely as the basis for calculating the schedules. Or has Victron fundamentally overhauled this feature in the last two months? If so, I must have missed it.

Imagine you are that person who has one little up3000 on your 5kVA. The max charge and discharge should be set to?

Capabilty and operating limits are two different things.

There are some circumstances when things can be exceeded.

And then from a different part of the dess manual.

Charge/Discharge Restrictions – You can also configure settings to control when your battery can charge or discharge to the grid. For instance, you may want to restrict discharging to the grid during specific times or days due to national laws.

I don’t want to argue, and I won’t. I’ve been running the DESS for 3 years now, including throughout the entire development phase. During that whole time, configuring the maximum charging and discharging power in the DESS has only ever served as a basis for calculations.

In this context, Victron means something else by charge and discharge limits. For example, completely preventing the battery from discharging, which is important for certain market restrictions.

But if you know better… then please go ahead. As I mentioned, I don’t want to argue, and my system is working.

I didn’t think there was a arguement here.

I was backing up this statement.

The thing is if you limit it over all, then it will never reach the potential it could possibly. Unless that is not the aim.

And the manual shows how to set the other limits of there are any restrictions needing attention. Some are set in the system itself.

And then there is the personalised use adjustments. Which will end up happening. The advice is good - start somewhere and see if it suits. Then adjust. Everyone is different.

Good evening,

The system is installed between the house’s ‘street’ connection and the house, and I’ve set it up so it can reach its maximum values.

Charging the batteries from the grid alone draws almost 330 A — in accordance with Victron’s specifications.

When discharging, the current is limited to 3 x 25 A.

But what I was actually asking was what needed to be entered now, as that wasn’t clearly stated anywhere.

For now, I’ll stick with the values, taking the limiting factor of the MultiPlus units into account.

Thanks in advance for your reply.

I’m also having problems with the description/information.

I now have a MultiPlus II 6k5 (previously an MP II 3000), but it’s still too large for my connection (2.5 mm² cable - 18 metres).

The MP II 6k5 configuration has been adjusted to 15 amps.

It seems logical to me that the DESS settings should also have the adjusted values.

DESS limits are for crating schedules.
Actual limitation is managed based on schedule and all other restrictions.

If DESS battery limit is 2kW and your 240V AC limit is 10A (2.4kWh) , it will use 2kW.

If DESS battery limit is 10kW but your AC limit is 10A, it will charge at 2.4kWh.

If your discharge limit is 10kW but your consumption from buttery is 1 kW it will push to grid only 9kW.

—>
DESS limits are used to restrict the schedule.
All operational limits (DVCS, CCL, CVL, DCL, AC line) will be used while loaded from grid or pushing back to grid.

Start with 50% of minimum( inverter, charger, battery dis/charge) and observe the system.

I have 3xMP2 5000 with active cooling and 56kWh battery. I could discharge 13.5kWh or charge 11.5kW, but I set DESS limit to 6kW.
With 2kW/MP2 they efficient.

Good afternoon, I understand now.

Charging averages 16.4 kWh for me, so it’s even slightly higher than I’d calculated.

But I’ll leave it set to the calculated value, since the value entered is only used to estimate how long it takes to charge and discharge the battery.

When it comes to the battery’s maximum possible discharge current, with 3 Mp you need to set the current for each device to one third of the total current. Do the same for the charging current.

Good afternoon,

That doesn’t seem right to me.

All the batteries are wired in parallel as one large battery.

They are connected to the three MultiPluses via the Lynx.

When setting up Dynamic ESS, all three inverters (in a three-phase setup) are added together.

The actual charging current per MultiPlus is not relevant here.

The total limits entered are all used to calculate how quickly the battery can charge and discharge.