Now it’s clear the remautomaat isn’t doing anything.
It’s supposed to avoid the possibility of 10A PV + 40A battery overwhelming the 40A diffs, but the PV is connected to the wrong side for that, it needs to be connected on the grid side of the remautomaat, along with the battery.