I’m planning to build an offgrid system (no grid connection!) and have to choose between two device-combinations. The system is to charge an electric car without grid, single phase, 10A and 235V. There is a big LiFe battery 48V / 30 kWh and 6 kWp solarpanels (at two strings).
Victron MPPT RS 450/100 + Victron Inverter Smart VA 48/5000
I believe that the inverter can handle peak loads better because of the toroidal transformer. Right? And there ist a eco-mode, which consumes only 3W at standby.
Victron Multi RS Solar 48/6000/100
Only one device, cheaper than (1), smaller, lighter. But lower “max. PV operational input current” (13A instead of 16A). No eco-mode (consumes always 20W) and I don’t know how it handles peak loads without heavy transformer.
a) 8 Panels with 450 Wp, Voc 38.80V, Isc 14,35A, Vmpp: 32,35V, Impp 13,51A (touches the 13A operational input)
or b) 7 panels with 450 Wp, Voc 52.6V, Isc 10.7A, Vmpp 44.6V, Impp 10.1A (only 7 panels because of 450V)
String 2 has only 7 modules anyway, so there is no problem with 450V.
Overall the MPPT RS 450/100 would be better with less restrictions.
The Inverter RS 48/6000 supports only 1 solar string, not 2, and I need 2. I would have to AC-couple the second string (and buy a additional inverter for that).
Well, a Multiplus-2 48/5000 would be much cheaper than a pure inverter like the “Inverter Smart VA 48/5000”. Onlineprices 555€ instead of 866€. Both use copper toroidal transformer and should perform similar at peak loads (?). The MP2 offers more functions (which I don’t need) and is cheaper at the same performance class (?).
In an other community somebody wrote, he tried to charge his car with an cheap inverter, and the car stopped charging in the first few seconds because it thought the supply was too weak. Then he bought a inverter smart VA 48/3000 and it worked. Perhaps some cars act like peak loads while starting the charge.
The noise of MP2 or of “inverter VA 48/5000” does not matter, it will be outside the house in a shed.
For argumentation to the network operator it’s easier, if the device is not able to connect to the network at all than if it were able and I just don’t connect it.
So I will choose combination (1) of the first post. Thanks for the answers and new food for thought!
Lars