Hi there,
We’re seeing some interesting behavior with DESS, and wanted to seek feedback on whether this is expected, or an issue in our configuration.
Specifically, when the system is scheduled for “Grid to consumption”, we’re (a) correctly seeing consumption from grid, but (b) also seeing a consistent 400-700W discharge from the batteries. Is this latter behavior expected?
From the graphs below, you can see this discharge behavior causes SOC to slowly decline ~10% overnight, Going into the night, the target SOC projections were to keep the SOC flat (which can be seen in the remaining projections shown).
My underlying assumption is the system is trying to match “grid” use with “AC loads”, and invert just enough to make up for the idle consumption / losses of the Quattros. Though I’m surprised these aren’t accounted for in the target SOC projections.
Some details on the system below.
We have 4x 10k 120v Quattros, in a 2x2 split-phase configuration:
- Grid connected to “AC Input 1”, with all loads on the “AC Output 1”
- AC-coupled PV on the load-side of the system, monitored by a Victron VM-3P75CT meter
- 60kWh of Discover AES batteries, with a communicating Lynk II BMS (on latest firmwares)
- Cerbo GX on Venus Large v3.54
- Quattros on firmware v555, with the latest ESS assistant installed
We’ve successfully tested standalone ESS for the past few weeks with a grid setpoint of zero watts (i.e., the system stores all excess PV and then discharges during low PV / evenings until the min SOC is reached – with minimal export/import in the meantime). Importantly, once min SOC is reached, the batteries idle around +/- 1 amp (so overnight, the batteries remain around the min SOC +/- 1 to 3%)
Our utility provider has a peak / off-peak pricing scheme, so we’re testing DESS in Green mode, with a fixed tariff schedule.
- In DESS settings, we’ve inputted the max discharge rate of the batteries (per what we’re seeing reported by the BMS), and max charge rate (per what we’ve set in DVCC). Maximum Power Import is set to 48kW (200A grid connection).
- We’ve also set the DESS system efficiency to 75% via Node Red.