I am sending -500w to modbus regster 37 on unitid 228 (VE.Bus)
To feed back 500w to the grid.
I am also reading back the value from modbus to ensure I had written it correctly, no issue here.
I am reading what I am writing.
But in actuality I am getting ± 857w feed back to the grid.
I dont understand why, when checking the VRM I can see Critical Loads being added to the grid feedback?
Can I disable the critical loads import ? I have connected the wiring up to AC OUT 1.
And ofcourse AC IN.
I would expect if I send -500 that I would get approximately -500 feedback to the grid.
I dont understand why this “Critical Load” is also added ontop of the feedback, generating a surplus on the requested feedback.
I would be very happy if only the left side was fed back (-480).
Any ideas how to improve or how other people deal with this ?
I must be missing a big clue or have something misconfigured.
If it is normal behaviour can you please explain the logic behind it so I can take it into account when steering the charging/discharging of the battery.
@DuivertNL I have removed the bridge between AC IN and AC OUT 1.
Looks alot better now, I did read the manual but failed to find the info on which AC the feedback would occur, apparently it can just go out on the AC IN.
@DuivertNL the MK3 is just connected and wired through a cable gutter to an electric box, if I need it I can just grab it from there without needing to unscrew the Multiplus at the bottom again, I had already noticed it goes into “Blocked” when MK3 is connected.